03/12/2009 5:26 AM
Why we earthed one secondary terminal of current transformer
Good Answers: 103
Re: current transformer earthing
03/12/2009 7:04 AM
Why you earthed the best judge is you,
But why you should earth:
CT , What about VTs (Voltage transformers ?)
In case one terminal is not earthed (or in some cases connected to common neutral) what will be the voltage on secondary of both the transformers ?
If the emf across secondary coils is Vs, (whether CT or VT)
then terminal 1 is at Vs1 and terminal 2 at Vs1+Vs
What is Vs1 ?
Additionally the OC of CTs create an extremely high voltage on secondary. Also the insulation of the CT is relatively weak earthing takes care of a bit of safety aspect too.
03/13/2009 1:05 AM
dear,
Earthing of CT secondary common wire is just essential as is required for Transformer neutral . This shall eliminate the neutral of CTs ( Common ) being floated / circulated
under un balanced conditions / failure of any one CT. Each phase of CTs shall correctly read the current.
This shall eliminate the dangerous over voltages being developed by circulating neutral - & in turn prevent bursting of CTs.