Heat Recovery Sizing for an Aquatic Center Air Handler

03/13/2009 12:43 AM

I need to size a run-around system for a single air handler which services an aquatic center. There are two pools; one therapy pool and the other is a 8 lane lap pool. The deck air temperature log indicates the room air temp stays around 80 deg F. The air handleing unit has handles about 17,000 CFM according to our flow measurements. Presently the unit takes in 100% OSA heats it up sends it into the building and exhausts 100%. It is located in Vancouver WA. I am having a difficult time sizing the coils and selecting a pump size. The coils need to be coated due to the chlorine atmosphere because it will corrode regular aluminum ones.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: May 2005
Posts: 244
Good Answers: 18
#1

Re: Heat Recovery Sizing for an Aquatic Center Air Handler

03/17/2009 12:42 PM

Max -

First things first.

17,000 CFM of outside ventilation air is sufficient to meet the IMC requirement for a 34,000 Square Foot pool and deck area.

Is your facility really this big? If not, your first order of business is to fix the massive energy drain caused by improper mechanical design of this system that is resulting in zero recirculation of air and 100% outside air.

A 100% Outside Air design is fine if desired, but then the supply air = OSA = Code requirement of 0.5 cfm/sf. No more, no less, and THEN you pretreat that 100% OSA by running it through a poly Heat Recovery core section (counter/cross flow) or place a coil in both the exhaust and the return air ducts to do the same.

If it is too late to reconfigure this to stop this massive waste of energy, and you are just doing retro- work, I would still recommend putting a VFD on the supply fan.

Once you have your airflows corrected, then have a discussion with a refrigerant-based coil supplier engineering rep.
You may well have a great opportunity here to do energy recovery with a lower pressure drop by using a mechanical refrigerant system to vapor/condense more efficiently than a "pumped" system, by which I presume you mean hydronic:water+antifreeze.

A refrigerant heat recovery 2-coil system would be sized by the supplier for you based on the physical size of your exhaust/return duct with the airflows involved. You may or may not need to place a compressor, accumulator, TXV, etc. inline as a powered mechanical system, since it is possible, depending on the temperatures involved, that you may get away with a passive evaporation-based system if this is a unitary packaged equipment installation.

__________________
Call it 'half empty' or 'half full' if you must, I've got the other half in a redundant glass...
Register to Reply
Active Contributor

Join Date: Mar 2008
Posts: 15
#2
In reply to #1

Re: Heat Recovery Sizing for an Aquatic Center Air Handler

03/24/2009 4:04 PM

Thank you for the wake-up. I must have had a brain block. I'll get started on the air flow correction right away. Thank you again