Anonymous Poster

Transformers - Calculating the HT Fault Level

03/13/2009 1:13 AM

Dear sir

i can calculate the fault level at the LT side of the transformer but not able to undersatand how to calculate ther fault level at the HT side of the transformer plz reply

raja sen

manager maintenace & Utility

Parakh agro Industries limited

India

mail id: raja_sen47@rediffmail.com

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#1

Re: How to calculate the fault level at the HT side of the transformer

03/13/2009 7:18 AM

Hi there,

Prospective symmetrical (Short Circuit) current = Short Circuit Level / (Sqrt(3) * voltage)

Cable Short Circuit Current = (Cross Section * K)/Sqrt(t)

Where K = 115 for copper conductorss, paper insulated.

t = time to withstande short circuit current

goto www.aberdare.co.za and download their cable facts and figures handbook. It gives the answers to all these and more. Beware - these standards/codes are applicable to South Africa and may vary in your country!

Regards,

Craig

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Transformers - Calculating the HT Fault Level

03/14/2009 5:10 PM

You do not have the information to make that calculation. Check with the utility. They should be able to give the the fault current at the point you require.

Reply
Associate

Join Date: Feb 2009
Posts: 47
Good Answers: 2
#3

Re: Transformers - Calculating the HT Fault Level

03/14/2009 7:20 PM

Please reference the National Electrical Code article 450 for guidance.The requirements vary, based upon primary voltage and the transformer impedance.It varies from 300% to 600% of the primary current rating for Circuit Breakers, but for fuses, it is 300% of the primary current rating, for tranformers over 600 volts.

If less than 600 volts primary, reference table 450.3(b) it varies from 125% to 250% depending on the rated primary current, whether it is internally protected, and the transformer impedance.

If the NEC is not available in your area, please provide data plate info from transformer and I can help you more.

__________________
"I See" said the carpenter as he picked up his hammer and saw.
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4
In reply to #3

Re: Transformers - Calculating the HT Fault Level

03/14/2009 9:38 PM

He is asking for the primary fault current. I don't see where you suggestions apply.

Reply
Anonymous Poster
#5
In reply to #4

Re: Transformers - Calculating the HT Fault Level

03/14/2009 9:57 PM

I stand corrected.

I misread the OP question.

Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#6

Re: Transformers - Calculating the HT Fault Level

03/16/2009 1:40 AM

Hi all,

I also misread the question - I gave a formula to calculate the fault current of the cable on the HT side.

My apologies.

As stated earlier - you need to get the impedance.

There are four methods you can use (depending on the accuracy you require)

1. Ohmic method

2. Per-unit method

3. Computer software

4. Point-to-point method

A simple way is as follows;

R=V/I = source impedance

where V = primary voltage and I = primary current

Conductor resistance / number of conductors = conductor impedance

source impedance + conductor impedance = total impedance

Primary voltage / total impedance = Short circuit current (RMS)

The conductor impedance you would have to look up in the relevant tables peratining to the codes governing your country.

Regards,

Craig

Reply
Anonymous Poster
#7

Re: Transformers - Calculating the HT Fault Level

03/16/2009 2:18 AM

hi for short ckt calculations get the ETAP software .this will help 2 u

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#8
In reply to #7

Re: Transformers - Calculating the HT Fault Level

03/17/2009 10:09 AM

This depends on your system.

If the HT supply is directly from utility, the answer given by wareagle is correct. You need to check with utility company; otherwise the fault current has to be calculated using any of the methods such as Per Unit, MVA Method or using Software like ETAP (www.etap.com), Easy Power (www.easypower.com), SKM Tools: DAPPER (www.skm.com) etc. However, for calculating fault, you have to have sufficient data of your system.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply