Anonymous Poster

33kV cable problem

03/14/2009 9:29 AM

Hi everyone,

In my company there is grid connection of 33kV.

Whenever i charge the circuit breaker of my side yard , at the same moment the circuit breaker of the goverment side yard trips .Both are VCB.

I have meggered the cable with 10kV digital megger.What i found was that the megger value of one phase is very low i.e 14.7 mega ohm.C.Ts and P.Ts have also been checked they are allright .Is it possible to locate the fault without digging out the cable if yes then ;how can i locate the exact location of the fault in the cable . Is there any method to calculate the location of fault in cable in meters , if yes then pls let me know.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: 33kV cable problem

03/14/2009 6:26 PM

What type of protection you have? What relay operates when it trips?

Did you meggar between each of the core of the cables and between each core and earthing (grounding)?

The meggar value you indicated is low but it is not that bad.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Active Contributor

Join Date: Apr 2007
Posts: 14
#2

Re: 33kV cable problem

03/15/2009 3:50 AM

what are the things connected your VCB out put side,[i think pt,ct,and transformer]

isolate one by one and megger the cable and find out the value,otherwise disconnect the vcb out going cable anther end and check the cable,if cable is ok and then check other connected things, finely transformer bushings and transformer winding.

anand ck

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: 33kV cable problem

03/15/2009 8:22 AM

Some more inputs are required.

1) After you close your side ,utility side vcb trips-OK did you try to close utility VCB-what is happening?

2) The utility VCB trips under what fault-UV/OV/OC/EF can you inform us?

3) Is your VCB connected to a transformer ,if so what is the rating of the trasformer and what are settings of protective relays

4) does trippings take place repeatedly or now only ?

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru
Popular Science - Cosmology - New Member

Join Date: Feb 2009
Location: Halcottsville, NY
Posts: 665
Good Answers: 16
#4

Re: 33kV cable problem

03/15/2009 9:21 AM

A Hipot megohmeter with a full wave bridge will give you an approximate location. An Underground Cable Fault Locater used by power companies progressively burns out the fault using high amperage. This is then followed with a high voltage capacitor discharge. The result of all this expensive hardware is something like the report from a pistol shot. Use a stethascope to find the exact location.

Batteries not included.

__________________
De gustibus non est dispudandum.
Reply
Associate

Join Date: Feb 2009
Posts: 34
Good Answers: 4
#5

Re: 33kV cable problem

03/15/2009 5:59 PM

You also need to check if there is any synchronisation or out of phase issue. A simple phase rotation check is often forgotten.

If you are trying to parrallel 2 transformers or feed one transformer from another you need to study the circuitry to ensure you have not created the problem by the way it is set up eg an earth point at one end that is seen as a fault by the relay at the source end.

I also agree that checking your protection scheme is a good idea as there may be a fundamental error in how it is set up.

If it is a cable problem the OMNICRON & BAUER have instruments that can detect the cable fault & give an estimate of where the fault is along the cable length. However, my experience is that if it is a newer installation then start looking at the cable terminations & connections first, human error is often a source of problems.

__________________
Murphy was an optimist....
Reply Score 1 for Good Answer
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#6

Re: 33kV cable problem

03/16/2009 5:01 AM

i think your cable is ok you shold check all wiring dig of your vcb

Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

anandck (1); dineshpandit80 (1); KRW43 (1); msamad (1); ramvinod (1); Tippycanoe (1)

Previous in Forum: Solenoid   Next in Forum: solution

Advertisement