earthing

03/15/2009 7:48 AM

Dear Member

i have a 110vac ups supply to my dcs and plc system.this is a floating supply and the voltage across phase and earth was 48 volts. after 3 months when I again measured as a part of preventive maintenance it was 3 volts. how this change can occur. will it affect the output current of the said ups.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#1

Re: earthing

03/15/2009 7:42 PM

Your supply might not be floating any longer. If one leg has found an earth point, you will certainly know it when a second leg finds earth. CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#2

Re: earthing

03/16/2009 4:42 AM

kindly check neutrel to earth voltage if it is more than 2 to3 volt then it may dangerous for your system in that case check your earth resistance and also check neutrel of your voltage it is a serious metter of electronics item serve from your UPS