How to solve the water hammer?
A pump (Spec. =400 M3/hr, head 50 meters) is running at 5.0 kg/cm2 and 400 M3/hr of 70 degree C waste water from a open tank, the pump outlet through a 10 inches check valve, manual valve and level control valve then 300 meters long (under ground and pipe rack) of 10 inches pipe to the inlet of a cooler. The control valve minimum opening is set at 25% to keep the minimum flow at 130 M3/hr. When the water tank level lower than the set point (50%), the control valve opening is down to 25% and flow is 130 M3 only, if the level down to 20%, the pump has to stop.
There are 2 other streams of the waste water (70 C) are going to the cooler at the same time, the back pressure of the cooler is about 3.7 kg/cm2 normally.
Symptom:
After 15 seconds from the pump is stopped, a big pipe hammer and structure vibration with the sound are found for a few seconds around pump area..
Do any suggestion for me? Please!
Robert Su 090317
Re: How to solve the water hammer?
03/17/2009 12:03 AM
Install an SMC with pump control and it will eliminate all water hammer and protect your pumps, pipes, valves and motor.
"Real Bass Players" do not use picks
03/18/2009 12:10 AM
GA!
03/18/2009 2:43 AM
What is SMC please?
07/13/2010 9:05 AM
Hi,
I think the best solution for this problem is installing VFD for motor.
So we can control both of water folw with pressure. VFD will solve all water hammer
pumps,pipes,non return valves & valves.
Best Regards,
Mahmoud
Good Answers: 266
03/17/2009 6:56 AM
The hammer could be the check valve closing if there is a great back flow after the pump stops. Change the type of check.
03/17/2009 7:29 AM
The changing the check valve will not solve the problem, but it is part of the problem. Pepsi had a very similar problem with water hammer so bad they were breaking pipes. I had them install an Allen Bradley SMC with pump control and it solved their problem 100% and in fact Guy said that when the system shut down, he could hear the check valve close and no water hammer at all. They have since installed many of these on all of their pumps and have 0 water hammer.
It's a very cheap way to eliminate water hammer, save your pipes, valves, motors and any other equipment you have in your system.
Check out www.ab.com look for SMC's, but also SQD makes them Benshaw makes them. You don't have to use AB, this is just what I used to handle. Just make sure you add the pump control and you will be all set.
Also you don't need to remove current motor starter, actually it is advised to keep the existing motor starter in place with the heaters.
03/18/2009 12:10 AM
GA!
03/17/2009 7:54 AM
Agree. Change it with Disk Check Valve(spring actuated).
ducon(am on somebody's elses computer n not logged in)
Re: Water Hammer Problems
03/17/2009 11:03 PM
Hi Robert,
In my experience with water treatment, Water Hammer issues shuold be managed by slowing down the start-stop speed of the fluid flowing in the pipes.
Water Hammer is caused by the momentum of the water moving in the lines suddenly transferring to other forms of energy. Because the water is suddently stopped, the energy is expressed as pressure waves up and down the water line, often putting physical stresses on the pipe mounting or even the pipe itself.
The suggestions given above are good, using a soft-starter (AB SMC) will slow the start-stop velocity change of the water (and hence spread the momentum change of the water over a longer period).
If you've got the cash, a better solution would be a variable speed drive for the motor. With this you could tailor the ramp up and ramp down times to minimise the water hammer, while keeping efficiencies.
This could also be seen as an investment, as the control valve could be removed. The VSD could handle the control of water flow (signal it to the level tranmitter in the tank).
This would save significant energy costs, as the pump would consume far less energy (as pressure is not being burnt by the control valve).
Other ways of minimising water hammer are;
1) look closely at the process, specifically actuated valve opening and closing sequences. Out of sync timing can also cause this.
2) Look at acutated valve opening and closing times. reduce hammer by slowing down valve opening and closing times.
3) Look at the structural supports of the lines. Loose or improperly supported lines will make noise no matter how smooth you make the process.
But ideally you should solve the hammer without having to reinforce the lines. Allowing this problem to endure willl eventually cause failures.
Good Luck
Anthony
03/17/2009 11:45 PM
Dear Anthony:
Thanks a lot for your detail explainations.
I will try to do what you suggested, and send any results if it is available.
Regards
Robert Su 090318
03/18/2009 12:09 AM
GA!
03/18/2009 12:11 AM
GA!
03/17/2009 11:33 PM
Robert
You have not specified the elevations of various items in the water circuitary. As water hammer phenomenon occures after about 15 seconds of stopping motor, I think, it is nothing to do with pump starting method (SMC). I suppose, the cooler should be at higher elevation than the pump and the sump, and the water must be reversing its direction towards pump and sump. In this reversal, obviously the check valve will close and water is forced to stop suddenly creating water hammer.
If this is the reason, closing the check valve little slowly will solve the problem, Or else, you may provide some buffer air chamber to absorb the water hammer energy, which should solve the problem. (This is very old technology, still best technology)
03/18/2009 4:53 AM
Quite accurate this system works pretty well It comprises a vessel with some air diaphram pressurised to sme pressure above the TDH OF THE PUMPING STATION and this overcomes the back flow pressures
03/17/2009 11:48 PM
Use the axial flow check valve (NozzleCheck valve) to eliminate the water hammer. The NozzleCheck uses a short stroke, fraction of an inch movement and springs to close the disk at the Vmin (minimum velocity as the fluid reverses). This solution is minimum cost and most troube free. No motor control or power.
03/18/2009 12:18 AM
Hi Robert
Placing a piece of flexible rubber hose in the line often solves the problem, as it is caused by the liquid trying to expand the tubing and then the tubing contracting back.
Tony
The nice thing about Standards is there are so many to choose from.
03/18/2009 4:42 AM
Please contact with manufacturers of :SHOCK, SURGE and WATER HAMMER
PIPELINE SHOCK PREVENTION.
• Surge Alleviators for Pipeline Water Hammer, Surge, and Shock
• Pipeline Shock Alleviator, Surge Attenuator, and Water Hammer ...
Looking at a simple schematic with a centrifugal pump, several alleviators can be used to guard you against startup surge, resonant pump shaft deflection and valve closure shock.
1. Reservoir
2. Centrifugal Pump
3. Motorized progressive Valve - Open when pump starts, then close as pressure begins to fall. Avoids acceleration head surge. Open when pump is stopped to prevent vacuum into which liquid rushes back and causes shock
4. Vacuum Breaker - valve used where pump may be stopped suddenly and there is no power for an item 4. to be opened
5. Pressure Instrument taping - Pressure over time traces taken at this point
6. Startup Surge Alleviator - JUMBOFLEX by SHOCKGUARD Ltd. for surge free "soft start"
7. Resonance Decoupler - WAVEGUARD by PULSEGUARD Ltd. stop system response damaging the pump, decouples pump from system
8. Block valves - Liquid over pressure, from expansion
9. High Temp Expansion compensator - Volume compensators by SHOCKGUARD Ltd. LIQUIBELLO all metal, or FLEXORBER with EI DuPont TEFLON
10. SURGEGUARD by SHOCKGUARD Ltd. low pre-fill, high compression ratio units for valve slam water hammer prevention
11. Emergency fast shut down valve
03/18/2009 10:41 PM
GA from me. It is full description of what I suggested in my post.
03/18/2009 8:02 AM
Let's cut the crap and all the fancy names............install a suitably sized pneumatic or bladder type accumulator!!!!!!!
03/18/2009 8:48 AM
I have solved the same problem in a slightly larger system with an 8 mile pipe run. The water hammer takes place across a little time and the reaches a quik apex. I used a Cla-Val pilot operated pressure relief valve, I was pumping 3500 GPM in a 24 inch Diameter pipe. I used a 10 inch relief in the middle of the system and a 12 inch valve near the recieving end of the flow. The hammer never happened again.
03/18/2009 9:24 AM
Dear Robert SU,
As Mechanical Engineers, the other responders to this query know more than me. I do know on Civil Engineering pump applications, we use a dampener on all our check valves to delay closing time from 30 60 seconds. In a municipal distribution system, the rebound of the pressure wave from closing may take from 60 to 120 seconds. However, the longer the rebound time, generally, the more the pressure wave is reduced due to the numerous pipes and interconnections the wave travels through in a normal urban distribution system. If this is a one pipe system with few fittings, the returning pressure wave can be significant and return time would likely be rapid.
Respectfully Yours,
Christian Cooper
03/18/2009 10:11 AM
Put into perspective, even if a small reverse flow is allowed by the check valve, it will create a significant force when the check valve slams closed. With 300 m of pipe downstream, there is roughly 15,000 kg of water in the pipe coming to an abrupt stop!
04/30/2009 4:59 AM
DEAR HI,
YOU HAVE NOT MENTIONED THA YOU HAVE INSTALLED A PRESSURE TANK PARALLEL TO THE SYSTEM OR NOT?
IF NOT THEN INSTALL A PRESSURE TANK OF SUITABLE SIZE ( AS TO BE CALCULATED) OF GET VERIFIED WITH ANY PLUMBING ENGINEER TO SELECT APPROPRIATE SIZE OF PRESSURE TANK.
United Arab Emirates - Member - New Member Engineering Fields - Piping Design Engineering - New Member
06/18/2009 8:44 AM
Try using air cushion check valve, this will solve your problem. I suggest you may contact the supplier or manufacturer for further information.
graysurpa