earthing strip

03/17/2009 6:06 AM

how chhose earthing strip according to breaker ampere rating?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: May 2008
Location: Bangalore,India
Posts: 10
#1

Re: earthing strip

03/17/2009 11:14 PM

Dear friend

No earth wire shall have a cross sectional area less than 3.0 sq.mm copper and 6 sq.mm if it is of galvanised iron or steel except in portable equipment whose current carrying conductor has a cross sectional area less than 3 sq.mm.

In such a case the earth wire should have a cross sectional area equal to current carrying conductor.

Please refer standard earthing practice ( if you are in india it is IS 3043) for more info.

Bhushan