Current Transformers for 400 kV System

03/17/2009 6:04 AM

Pl clarify in the 400kV system with one & Half Breaker arrangement, 3 CTs instead of 4CTs are acceptable? Any limittations or drawback with 3CT arrangement? Pl clarify

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#1

Re: Current Transformers for 400 kV System

03/18/2009 5:57 AM

The one and & half breaker arrangement uses 3 breakers for every 2 circuits. Now every breaker needs a CT so you get 3 CT for every 2 circuits. 4 CTs are needed in the 1.33 breaker/circuit system which uses 4 switching units for every 3 circuits. Eventually the 1.5 Breaker system has 3 CTs.

__________________
The time is ......now
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2

Re: Current Transformers for 400 kV System

03/20/2009 7:48 AM

Check how 3 cts will help.. I understand 4 cts are very much required.

__________________
BNDas
Register to Reply Score 1 for Off Topic
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#3

Re: Current Transformers for 400 kV System

03/20/2009 9:17 AM

Dear Raggul,

Please note that in general, according to your applications the number of CTs is decided. However, nothing is stated that 3 CTs instead of 4 CTs in one and half breaker scheme is the acceptable system. Maybe it is the minimum acceptable scheme but not the optimum one.

The control, metering and protection schemes of the one and half bus configuration is the most complicated one with regard to CT coordination and wiring.

Each CB in the one and half configuration has CTs on both sides. The middle CB is the one which has the largest number of CTs on both sides. Because, it has to coordinate with the outer busbars breakers.

Therefore, as previously mentioned according to your scheme of metering and up to which level of reliable and redundant protection scheme is required, you can decide the required number of CTs.

Best regards,

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#4

Re: Current Transformers for 400 kV System

03/22/2009 1:01 PM

3 ct will only work if the third ct has the capability to replace the 4th ct. This is given by the number of the secondaries needed, rated power.