DOL starter for 75kw Chiller compressor

03/17/2009 9:08 PM

Dear All electrical specialist,

One of my client has requested me to install DOL starter for his chiller compressor 75kw 380v 3phase 60Hz. His main power supply is from 1000 Kva 380V 3ph 60Hz diesel generator,which is already at 600 Ampere loaded.

Can i install DOL starter for this 75kw Chiller ?

Thank you and Best Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: DOL starter for 75kw Chiller compressor

03/17/2009 11:04 PM

Yes. If you perform your power calculations to find the generator current and compressor current you will find that there is enough generator capacity in reserve (even taking into account an estimate for the high inrush current DOL starting of a compressor motor).

Do you know what the DOL starting current of the compressor is?

__________________
jack of all trades
Reply
Anonymous Poster
#3
In reply to #1

Re: DOL starter for 75kw Chiller compressor

03/18/2009 2:08 AM

Thank you very much Jack of all trades,DOL starting current is x7 of the compressor full load current, in my case is 130A. ; 130A x7 = 910 Ampere.

Regards

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #3

Re: DOL starter for 75kw Chiller compressor

03/18/2009 2:17 PM

This is a little high to be trying to start off the same loaded generator. As others have suggested, you will need to either use a soft start circuit or start the compressor first before loading up the generator.

__________________
jack of all trades
Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#7
In reply to #1

Re: DOL starter for 75kw Chiller compressor

03/18/2009 7:27 AM

dear,

DOL starting current of the compressor is 8- 10 times * rated motor current.= 1340 Amp

__________________
Exploring the Science of Electricity
Reply
Anonymous Poster
#2

Re: DOL starter for 75kw Chiller compressor

03/18/2009 12:48 AM

DOL starting will draw a heavy current 3 to 6 times its normal current and for 3 to 15 seconds in unloaded that is on suction stroke but if it is on compression stroke it will take more time to start and in that case voltage wiil be low for other equipments. For rotary compressors if you have suction side vane control u can use a DOL but still not good.

Suggested methods without knowing load details are

Yes u can unstall a DOL starter wiyh soft start method ,slow increasing voltage, constant frq. for rotary OR one with V/f constant rise starter vary volt and prop freq for reciprocating OR a dynodrive. for unloaded unit/bypassed unit

If your chiller compressor is having a bypass solenoid valve bet suction and delivery that can be opened for 10 seconds by a timer.

Try this and for equipment details and order undersigned can help as a consultant or supplier on charge basis.

Write to,

Mr. Kulkarni Yashwant

12 Monidan Apptt

Mulgaon Church Road

Tamtalao

VASAI CITY 401 201

Near Mumbai Maharashtra State INDIA

Call me ys uncle on +91 94224 754 11 0r email on yskulky@rediffmail.com for further paid solutions. BEST LUCK

Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#4

Re: DOL starter for 75kw Chiller compressor

03/18/2009 2:24 AM

dear,

with longer perception, even if it is possible to start the motor DOL with the existing 1000kva dg, it is not advisable to permanently do the same, as

1. chances of alternator winding burning during stalled motor conditions. even though the breaker / mccb may have been provided.

2. higher curremt transients on the supply system - increasing Demand with rise in demand charges.

3. Life of mechanical equipment goes on reducing due to higher starting torque jerks.

SUGGESTED....

1. HAVE AUTO TRANSFORMER WITH DOL.... AFTER 6-9 SEC. GOES TO MAINS LINE & AUTO TRANSFORMER IS BY PASSED.

2. HAVE VFD .... REDUCES MONTHLY KWH BILLING BY ATLEAST 8 % AS THE CHIILER LOAD IS A CYCLIC LOAD. RUNS EQUIPMENT AT PF>0.93, REDUCING DEMAND AS WELL AS DEMAND BILLING.

REGARDS

__________________
Exploring the Science of Electricity
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: DOL starter for 75kw Chiller compressor

03/18/2009 4:06 AM

3. Install a soft-start.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#6
In reply to #4

Re: DOL starter for 75kw Chiller compressor

03/18/2009 5:07 AM

4. remove 600A load

5. install star/delta starter

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#9

Re: DOL starter for 75kw Chiller compressor

03/18/2009 10:53 PM

Apart from the starting KVA the acceleration time is very important whcih depends upon the inertia of the rotating systems.Longer the time duration of starting current will last longer (though it will be drooping)The voltage drop due DOL starting has to be determined as motors are designed to accelerate at 80% rated voltage .The TVD of the generator with preseent loasd will indicate this.The compressor does it start and run continuously or will have frequent starts and stops .These are additional points to bear in mind in addition what has been said in other posts.

__________________
To avoid crticism do nothing,say nothing,be nothing