Problem Measuring Thyristor Gate Signals

03/19/2009 1:10 AM

Dear All Gurus,

One of my technician using Osilloscope proble with 20M Ohm input impedance to check the running thyristor gate signal at the 2 lead cables,one lead to gate and other to anode (Red and Yellow small cable) Suddenly all the incoming 450A HRC fuse for 12 unit thyristor are blown x12 units.

This 450kw 400v DC drive thyristor system is for rolling bar steel mill.

May i know why this signal measure can caused such big explode ?

Osilloscope is power from external source than the control panel.

Thank you and Best Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 450KW 400v DC drive thyristor explode

03/19/2009 4:08 AM

Was there an isolating transformer between the oscilloscope and the local single phase supply powering it? It sounds like your technician accidentally grounded the thyristor output using the ground-referenced ground probe lead causing a low impedance (high current) phase to ground fault, resulting in the explosion and blowing the fuses.

__________________
jack of all trades
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#4
In reply to #1

Re: 450KW 400v DC drive thyristor explode

03/19/2009 5:01 AM

This may be the case as poster is writing, he measured between anode and gate. Imagine whats going to happen if un-isolted ground wire is on anode?

Register to Reply
Power-User

Join Date: Jan 2006
Posts: 377
Good Answers: 2
#2

Re: 450KW 400v DC drive thyristor explode

03/19/2009 4:39 AM

Brings back memories for me. If the internal oscilloscope circuitry was definitely isolated from the test circuit, I would be wary of probes slipping off of components. I had to place heat shrink tubing over my probe tip except for the very, very end to prevent it causing shorts in the circuit under test.

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#3

Re: 450KW 400v DC drive thyristor explode

03/19/2009 4:49 AM

What is the specified min firing current of Thyristor? In my opinion you should have measured between ground and gate. and also thyristor should have been unloaded before any measurements.

if anode was at 400 volts,20 MΩ can pass 0.4mA through gate,not sure if it can fire thyristor.more info about circuit may help.

Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#5
In reply to #3

Re: 450KW 400v DC drive thyristor explode

03/19/2009 11:55 PM

Dear Rakesk Semwal,

Thanks for advise , Igt is 300mA AND IL is 800mA.

May i know why if i measure ground and gate may cause explode ?

Regards

Register to Reply