Dear ALL
does any body explain grid tesistence and pit resistence calculation of earthing.Let we have following valu of earth pit resistence
  1. p-1=0.25
  2. p-2=0.35
  3. p-3=0.5
  4. p-4=0.20
What will be valu of grid resistence. What is procedure to connect pit in series & what is procedure to connect in parrell
Re: grid and pit resistence
03/21/2009 7:38 AM
Dear,
By Ohms Law,
Resistances in parallel have 1/ Rt = 1/R1 + 1/R2 + .... + 1/Rn
Grid resistance 1/Rt = 1/0.25 + 1/0.35 + 1/.5 + 1/.2 = 13.857 Mhos
Grid Resistance Rt = 1/13.857 = 0.072 Ohms.
Practical measurement errors if you consider, then actual mesured value shall be within 10% of your above calculations.
Grid resistance or any individual pit resistance can be measured by 3 electrodes method, instruments called Earth testers are available for the same.