40 MVA 132/22kV Substations

03/22/2009 9:56 AM

Approximately, how many Secondary 2MVA 22/0.415 kV substations can be connected to a 40 MVA 132/22 kV Primary Substations?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: 40 MVA 132/22kV Substations

03/22/2009 10:04 AM

Without having load and demand information, this is an impossible question to answer and any answer is nothing more then a guess.

You need to design this system based on the load you need to provide for.

Register with this forum will you please.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: 40 MVA 132/22kV Substations

03/22/2009 3:09 PM

Approximately 20.

Please note that this is a discussion forum, not a free engineering consultancy service. For a more detailed analysis and an answer that will suit your particular site, you MUST consult your local electrical engineering design or consultancy group for a real answer.

__________________
jack of all trades
Reply
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#3

Re: 40 MVA 132/22kV Substations

03/23/2009 12:53 AM

Dear Friend,

40MVA 132/22kV substation came up with definite analysis, demand and connected loads. Check the LV, which required 415V and below.

* Make LV load analysis based on LV demand and connected loads.

* From here, you can sum up all LV loads, then convert this to kVA or MVA

* Once you have this, divide this to 2MVA, whatever the result(s), then "YOU HAVE THE NUMBER OF 2MVA SECONDARY XFMR.

Eren

Reply Score 1 for Good Answer
Participant

Join Date: Mar 2009
Posts: 1
#4

Re: 40 MVA 132/22kV Substations

03/28/2009 6:25 AM

Since this is a hypothetical question, then not more than 20 secondary s- stations due to the power equation. However this is to be determined by potential drops owing to supplying close to load centres and conductor length/type as this leads to power losses.

cheers

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brooks Wamala (1); ereneduarte (1); jack of all trades (1); North of 60 (1)

Previous in Forum: cable testing   Next in Forum: Which motors require stator RTDs?

Advertisement