Axial Fan efficiency vs Centrifugal fans efficiency

03/23/2009 12:38 PM

Hi, Fan Parameters: 1. Flow: 3000 cmh, 2. Diameter: 350 mm, - For centrifugal fan: I can achieve following parameters: A. Pressure: 100 Pa B. Power: 160 Watts This means that efficiency of ~ 52%. - For axial fan: I can achieve following parameters: A. Pressure: 10 Pa B. Power: 180 Watts This means that efficiency of ~ 4.5%. Question: - Is there any mistake by me calculation of efficiency of axial flow fan? - If calculation is right? then why axial fan is so inefficient? - Even though axial fans are so inefficient, why it find these much applications? - Is there any other good efficient alternative for axial fan with high flow and low pressure? Regards, Keyur Shah

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/23/2009 10:36 PM

Can you show your calculations?

Do not have performance curves to easily see the efficiency points?

Reply
Associate

Join Date: Jan 2007
Location: Pune / India
Posts: 48
#2
In reply to #1

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/24/2009 12:11 AM

I have calculated efficiency with following formula: Efficiency = Pressure (Pa) x Flow (m3/s) / 102 x Power (kw)

__________________
First do it and then talk about it
Reply
Anonymous Poster
#3

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/24/2009 1:21 AM

Yes, there is a mistake with regard to the efficiency of the axial flow fan, unless the operating point is so far away from BEP that it would not work anyway. Axial fans are not so inefficient. I would guess that the mistake is more to do with the input figures than the calculation per se. The two duties you quote are substantially different.

When you say "I can achieve following parameters" does this mean within the same system, or that such fans are available or what?

Reply
Associate

Join Date: Jan 2007
Location: Pune / India
Posts: 48
#4
In reply to #3

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/24/2009 3:20 AM

Dear, I didnt understand your point. First, is there any other formula for calculation of efficiency of axial flow fan. Second: Input figures are 100% perfect, I have achieved this point from characteristic curves. Third: Also, I didnt got how two duties are substantially different. Request to give the solution. Regards, Keyur Shah

__________________
First do it and then talk about it
Reply
Anonymous Poster
#5
In reply to #4

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/24/2009 5:27 AM

Substantially different; 10 Pa discharge to 100 Pa discharge. If in the same system how can the flow be the same?

Request you give the data.

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4497
Good Answers: 137
#6
In reply to #4

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/24/2009 9:39 AM

keyur

Your calculations are OK but don't necessarily tell the whole story. You need to compare the best efficiency point for the 2 fans. Preferably check on several models of each type to give an overall picture. Also smaller machines tend to be less efficient as fixed losses are more significant etc.

Are you sure your measurements are accurate? 10Pa = 1mm w.g. and is not easy to read.

Cheers..........Codey

__________________
Give masochists a fair crack of the whip
Reply
Anonymous Poster
#7
In reply to #6

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/24/2009 8:40 PM

1 m.

Reply
Anonymous Poster
#9
In reply to #7

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 1:26 AM

Sorry mate, you were of course correct (1 mm) - sooooo glad I was not signed on.

Reply
Associate

Join Date: Jan 2007
Location: Pune / India
Posts: 48
#8
In reply to #6

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 12:11 AM

Dear, I am 100% sure because I got this details from curves. And many of our clients are using these fans for condenser cooling. Regards, Keyur Shah

__________________
First do it and then talk about it
Reply
Anonymous Poster
#10
In reply to #8

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 2:11 AM

Unless I am not understanding this thing, your units are wrong. As Codey pointed out 10 Pa is just over 1 mm water column. This you will not be able to measure with any accuracy.

You have given the discharge pressure but you do not give the suction pressure. If this is atmospheric pressure then your efficiency has so many zeros in front of it as to be meaningless.

The power required to raise the pressure by 10 Pa is negligible and you probably would not notice the difference between this and running the blower under no load.

Also as stated before these blowers appear to run in two different systems as the system resistance is an order of magnitude different.

Your calculation appears to be very simplistic and would be just about OK for incompressible fluids.

For Polytropic efficiency when compressing gases think in terms of Eff pol = n/(n-1) * (k-1)/k

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#11
In reply to #8

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 3:05 AM

Your calculations are correct and everything is OK but the efficiency .

Axial flow fans are typically supposed to run at around 50-60% efficiency under rated condition. On either side there will be sharp drop in efficiency.

Can you check up the rated cfm of the fan vis a vis the cfm demanded by the system ?

And axial flow fans are supposed to run at very low Pa so this Pa is OK for it (Consider the Axial flow fan at the ceiling , or the propeller or the exhausters - they are not supposed to generate much Pa)

Just a quick link however very less details, but does compare various types

http://www.engineeringtoolbox.com/fan-types-d_142.html

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Score 1 for Good Answer
Anonymous Poster
#12
In reply to #11

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 4:51 AM

sb,

With all due respect I believe that his calculations are not correct.

If you plug the numbers given into the calculator for pumps on the same site that you quote http://www.engineeringtoolbox.com/pumps-power-d_505.html you will see that it will not even give an answer to the power until you reduce the efficiency to some very low number.

I used 3000 m3/hr, assumed normal conditions so a density of 1.204 kg/m3 and a head of 1 mm.

If I have this totally wrong I would really appreciate learning where I am going wrong. Would also help the OP.

Reply
Associate

Join Date: Jan 2007
Location: Pune / India
Posts: 48
#13
In reply to #11

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 5:24 AM

Dear, Can you give me your email ID. I will send curves for both Axial and CF Fan to you. Regard, Keyur Shah

__________________
First do it and then talk about it
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4497
Good Answers: 137
#14
In reply to #8

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/25/2009 6:08 AM

Hello again keyur

Not quite sure what you're saying. Are your figures based on measurement or taken from curves?

I've just checked a couple of suppliers' data for axial fans on the web and they only give curves of flow vs pressure, not efficiency or power.

Your power calcs are OK, at these sorts of pressure rise the error caused by ignoring compressibility is negligible.

Also you need to be sure whether your pressures are static or total. 10 Pa dynamic pressure relates to an air velocity ~ 4 m/s, and fan discharge could be much higher than that. Some suppliers quote total discharge pressure, and if system requirement is calculated on static a well-designed transition piece (gentle taper) is needed to recover pressure.

Cheers........Codey

__________________
Give masochists a fair crack of the whip
Reply
Associate

Join Date: Jan 2007
Location: Pune / India
Posts: 48
#15
In reply to #14

Re: Axial Fan efficiency vs Centrifugal fans efficiency

03/26/2009 11:28 AM

Dear, This figures are taken from curves. And pressure mentioned by me is static pressure only. Regards, Keyur Shah

__________________
First do it and then talk about it
Reply
Associate

Join Date: May 2011
Posts: 27
Good Answers: 3
#16

Re: Axial Fan efficiency vs Centrifugal fans efficiency

05/14/2011 1:47 PM

I am trying to determine how to measure Axial Fan Efficiency and Centrifugal Fan Efficiency. I just posted a detail comment about centrifugal Fan Efficiency measurement and calculations. see

http://cr4.globalspec.com/thread/31413/Centrifugal-Air-Compressor-Efficiency-Calculation#comment727488

Once I determine how to measure enthalpy, will this method and formulas be applicable to measuring Axial Fan Efficiency as well as Centrifugal Fan Efficiency?

Reply
Reply to Forum Thread 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (7); Codemaster (2); Dug (1); keyur_197 (5); sb (1)

Previous in Forum: ways of Cleaning clays from gypsum   Next in Forum: Syntron Vibrators

Advertisement