Motor Control and Soft Starters

03/25/2009 12:55 AM

I got a crusher mill that is powered by one 90kW induction motor. The company suggested that I can use their spare 90kW motor in conjunction with the existing motor to upgrade the mill`s performance since it is under powered by about 60kW.

A method is to remove the existing 4belt pulley and fit an 8 belt pulley on it, then have the 2 motors on each side driving it with 4belts. The mechanics seems straight forward.

How do I start these two motors by means of soft starters? Any Ideas about the control circuit for this occation, and what about protection for different types of loading faults?

Can I use two soft starters to start two motors driving the same shaft or will the torque management of the one soft starter intervene with the same function on the other soft starter?

Can some GURU give me light on this please.

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#1

Re: How 2 control 2x 90kW motors driving a common shaft

03/25/2009 7:23 AM

Hi there,

I would definately look at using a VSD/VFD to drive the two tandem motors.

You can take a look at the Danfos website. Download one of the VLT manuals - and you will get the typical circuit you are looking for.

Just make sure you use shunts and chokes. With a VSD/VFD you can be more certain that the motors are getting the same reference.

I would not use a softstarter for this application. Different soft starters work in different ways. Some makes thyristors only fire on two phases and some on all three. Some do not offer complete isolation in the case of breakdown etc etc.

Regards

Craig

Register to Reply
Associate
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.

Join Date: May 2008
Location: Australasia
Posts: 26
#2
In reply to #1

Re: How 2 control 2x 90kW motors driving a common shaft

03/25/2009 1:29 PM

Good info, THANKS/DANKE

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Motor Control and Soft Starters

03/25/2009 5:43 PM

First off, you cannot just put two motors in tandem like that unless they are EXACTLY the same motor. Any slight difference in slip will cause one motor to drag the other one as a load, overloading the first one.

Secondly, VFDs are unnecessary unless there is an advantage to changing speed. The only kind of crusher that can take advantage of that is a Vertical Shaft Impactor (VSI), which will change the product size and efficiency with speed. A Horizontal Impactor, Jaw, Gyratory (Cone) or Pulverizer (Hammer Mill) will actually work WORSE with a VFD unless you always run at full speed, because they work on HP and as you reduce speed, you reduce the HP. then if you are always running full speed, you will be wasting energy and increasing your operating costs. Besides, only the most expensive of VFDs with a closed-loop torque follower control capability can work to prevent the dragging issue on mis-matched motors, and I don't think anything from Danfoss is capable of that. By the time you finish paying for the 2 drives and sophisticated controls it takes to do this, it would have been cheaper to buy a brand new 150kW motor.

If the 2nd motor is the exact same make and model as the existing, and the slip value on the nameplate is the same, you can do it with one large soft starter feeding 2 separate OL relays going to the two motors. Then you just wire the OL relay aux. contacts in series to shut down the soft starter if either motor over loads. It's done that way all the time.

If you need more help, call this guy in Christchurch, he is one of the most knowledgeable soft starter resources on the planet.

http://www.motor-control.co.nz/

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Associate
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.

Join Date: May 2008
Location: Australasia
Posts: 26
#4
In reply to #3

Re: Motor Control and Soft Starters

03/25/2009 6:31 PM

Cheers mate!

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#5

Re: Motor Control and Soft Starters

03/26/2009 1:09 AM

Hi all,

I said to use one VSD to control both motors. Of course I assumed that both motors were identical (assumption is the mother of all f#ckups).

I have used this configuration before - not for a crusher though. The Danfos VLT 5000 worked fine. Admittedly it is not cheap.

The VSD would work in closed loop tourque control.

As previously stated, there is a typical circuit in the VLT manual. They also give a few guidlines as to what setup is required.

Regards,

Craig

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments