What Causes High Voltage Between Earth and Neutral?

03/25/2009 12:31 AM

tell me what are the probable causes of high voltage beteeen earth to neutral and how it can be rectified.

__________________
In the journey of search.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Causes of high voltage between earth to neutral.

03/25/2009 4:13 AM

<...the probable causes of high voltage beteeen earth to neutral...>

  • Phase current imbalance caused by a large number of single phase loads applied to one phase elsewhere.
  • Long distance between the substation and the local earth point.
  • Poor earth connection at local earth point.
  • Poor earth connection at the substation.

<...how it can be rectified...>

Provided the local earth connection is doing its job properly, there is no need to bother. Everything else is the utility supplier's problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Cosmology - New Member

Join Date: Feb 2009
Location: Halcottsville, NY
Posts: 665
Good Answers: 16
#5
In reply to #1

Re: Causes of high voltage between earth to neutral.

03/26/2009 1:47 PM

Parrallel runs of differing potential (see ans. # 1) can be subject to 'mutual capacitance' . Cross the individual wires at all convienient points (contact is best), ie. junction boxes, terminations, etc..

__________________
De gustibus non est dispudandum.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: What Causes High Voltage Between Earth and Neutral?

03/25/2009 7:17 PM

When you say "between Earth and Neutral", where is "earth"? Is it a ground rod or the actual earth(dirt)?

Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#3

Re: What Causes High Voltage Between Earth and Neutral?

03/25/2009 10:51 PM

Balance phase loads and backfeed in circuit will lower.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4

Re: What Causes High Voltage Between Earth and Neutral?

03/26/2009 6:46 AM

There have been so many CR4 blogs on this subject in the past, why don't you research those first before going through the same process all over again......?

Once you have read all of those and you still have a question, we can address that for you.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#6

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 11:47 AM

Hi P1K2S3,

PW Slack's answer is a good starting point, the Nuetral and Ground should be bonded at the service enterance of the facility. The farther you get away from that point the greater the potential difference is in terms of resistance because of conduit capacitance of the wiring. The high voltage should not be present unless there is noise transients or spikes on the common mode (Nuetral to ground). Noise and spikes can be generated by equipment operating in the facility or by nature (like lightning strikes). Oneac makes a great line of power conditioners and ups equipment that solves this problem. Their equipment has an isolation transformer so the Nuetral can be rebonded to ground and a filtering circuit to shunt the transient current back to ground. This will eliminate the volatge differential from the electrical circuit and prolong the life of equipment prower by the power conditioner or ups.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #6

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 12:26 PM

My understanding is that the earth/neutral bonding may only be done at the substation transformer, nowhere else......double bonding being a big no no......!

Faint memory from 40 odd years ago........

See also:-

http://en.wikipedia.org/wiki/Ground_and_neutral

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#8
In reply to #7

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 12:31 PM

Hi Andy,

That is not true, anywhere there is a isolation transformer in an electrical circuit the nuetral must be rebonded to ground or the secondary side of the transformer will be floating.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #8

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 12:52 PM

Does that not in some way negate the isolation, bonding together? or do you mean the neutral and earth from that isolation transformer only....? Please explain....

I must admit I had not given any thought to isolation transformers.....

Also, where you are on this world may play a role with regards to rules & regs surely....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#10
In reply to #9

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 1:00 PM

Because there is no direct connection between primary and secondary windings of an isolation transformer all the conductors are floating and 1 point on the secondary must be taken to ground for the Nuetral point (exception corner delta where a line is grounded). It does not matter where you are.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #10

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 1:41 PM

Even rules in this area of the neutral were changed in the USA to save copper in WW2, but were only removed from the regs book in 1996!!!

It does play a role where you are, some countries have different ideas (note I did not say better!)

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#12
In reply to #11

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 2:04 PM

There are different materials used but Copper is the premium because of it conductivity.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #12

Re: What Causes High Voltage Between Earth and Neutral?

03/31/2009 4:16 PM

You don't say......

The USA saved copper by installing houses on 2 wires in WW2.......

Rules and regs are always changing and being refined. The world over.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #6

Re: What Causes High Voltage Between Earth and Neutral?

01/12/2024 6:11 AM

That would not be true for TT and TN-S connections.

Earthing system - Wikipedia

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 14 comments