Re: Causes of high voltage between earth to neutral.
03/25/2009 4:13 AM
<...the probable causes of high voltage beteeen earth to neutral...>
Phase current imbalance caused by a large number of single phase loads applied to one phase elsewhere.
Long distance between the substation and the local earth point.
Poor earth connection at local earth point.
Poor earth connection at the substation.
<...how it can be rectified...>
Provided the local earth connection is doing its job properly, there is no need to bother. Everything else is the utility supplier's problem.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Re: Causes of high voltage between earth to neutral.
03/26/2009 1:47 PM
Parrallel runs of differing potential (see ans. # 1) can be subject to 'mutual capacitance' . Cross the individual wires at all convienient points (contact is best), ie. junction boxes, terminations, etc..
__________________
De gustibus non est dispudandum.
Re: What Causes High Voltage Between Earth and Neutral?
03/26/2009 6:46 AM
There have been so many CR4 blogs on this subject in the past, why don't you research those first before going through the same process all over again......?
Once you have read all of those and you still have a question, we can address that for you.....
__________________
"What others say about you reveals more about them, than it does you." Anon.
Re: What Causes High Voltage Between Earth and Neutral?
03/31/2009 11:47 AM
Hi P1K2S3,
PW Slack's answer is a good starting point, the Nuetral and Ground should be bonded at the service enterance of the facility. The farther you get away from that point the greater the potential difference is in terms of resistance because of conduit capacitance of the wiring. The high voltage should not be present unless there is noise transients or spikes on the common mode (Nuetral to ground). Noise and spikes can be generated by equipment operating in the facility or by nature (like lightning strikes). Oneac makes a great line of power conditioners and ups equipment that solves this problem. Their equipment has an isolation transformer so the Nuetral can be rebonded to ground and a filtering circuit to shunt the transient current back to ground. This will eliminate the volatge differential from the electrical circuit and prolong the life of equipment prower by the power conditioner or ups.
Re: What Causes High Voltage Between Earth and Neutral?
03/31/2009 12:26 PM
My understanding is that the earth/neutral bonding may only be done at the substation transformer, nowhere else......double bonding being a big no no......!
Re: What Causes High Voltage Between Earth and Neutral?
03/31/2009 12:31 PM
Hi Andy,
That is not true, anywhere there is a isolation transformer in an electrical circuit the nuetral must be rebonded to ground or the secondary side of the transformer will be floating.
Re: What Causes High Voltage Between Earth and Neutral?
03/31/2009 12:52 PM
Does that not in some way negate the isolation, bonding together? or do you mean the neutral and earth from that isolation transformer only....? Please explain....
I must admit I had not given any thought to isolation transformers.....
Also, where you are on this world may play a role with regards to rules & regs surely....
__________________
"What others say about you reveals more about them, than it does you." Anon.
Re: What Causes High Voltage Between Earth and Neutral?
03/31/2009 1:00 PM
Because there is no direct connection between primary and secondary windings of an isolation transformer all the conductors are floating and 1 point on the secondary must be taken to ground for the Nuetral point (exception corner delta where a line is grounded). It does not matter where you are.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Good Answers: