How Do We Size a Generator?

11/14/2006 11:47 AM

What is prime and standby power? If the tcl = 100kW and mdl= 80kW. Now how do we go for a generator sizing?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Oct 2006
Location: Northern NY
Posts: 89
Good Answers: 4
#1

Re: How Do We Size a Generator?

11/15/2006 1:14 PM

Prime power rating is for when the generator is used for continuous power whereas standby power is for when the generator is used only occasionally. It is at a lower engine rating. The prime power rating is usually around 75 or 80 % of the standby rating. So the gist is that if a generator is to be used as prime power it needs to be bigger than one supplying the same size load on a "standby" rating. This is just an outline, I'm sure others can fill out more.

__________________
Never underestimate the power of stupid people in large groups.
Reply
Anonymous Poster
#2

Re: How Do We Size a Generator?

11/16/2006 4:33 PM

It is necessary to determine the load that is suitable for the application. The size is not necessarily the total connected load but is the maximum operating load plus a maegine you feel comfortable with.

Once the load is determined, apply the through put effeciency of the type of alternator you like to use to determine the input shaft kW requirement. Typical industrial synchronous alternators have through efficiency of over 90%.

Now determine the prime mover kW rating. This is wherer prime duty and standby duty comes in. Industrial engine manufacturer publish the ratings for each application with the auxiliary equipment power requirement.

After determining the prime mover rating and the duty, you can define the cooling (and heat recovery, if applicable) system to meet the requirement. Engine/Generator controls and distribution swtchgear will have to be desinged as per the engine and generator (alternator) in use.

Note that this is applicable for a single engine, isolated power source. If more than one engine-gen set is to be operated or connected to national grid, then other system requirements arise.

Hope this is of some help

pulto45

Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#3

Re: How Do We Size a Generator?

11/17/2006 3:04 PM

Rule of thumb is: 125% of demand load + 100% largest motor start expected = tcl.

For critical applications, add a safety factor, but keep in mind that efficiency suffers
when the generator is too much oversized. - It's a judgement call.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: How Do We Size a Generator?

04/29/2025 4:58 AM

The <...we...> simply picks up the telephone and discusses the requirement with <...generator...> manufacturers directly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JDknut (1); Pragmatist (1); PWSlack (1)

Previous in Forum: HT Cables: What Problems Do They Face?   Next in Forum: Motor Lead Failures

Advertisement