Dear All Electrical Gurus,
While i was a electrical contractor sometime ago,i had seen an 'abnormal' installation of power factor improvement in a Palm oil kernel crashing plant.As i asked the owner the reason of many capacitors is to reduce loading current during full machines running and also reduce the Max.Demand (our country is 30min interval)
In the kernel crashing plant they have 60 units (2sets x 30 units)of machine which is driven by 75kw 6P 415V 50Hz motor with AT starter panel and EACH install with 50Kvar pf improve capacitor at the Main contactor , Which is feed from 2 sets of 2500Kva transformer to 2 set of Main distribution 4000A , loaded with 3000A due to some machines were in maintenace etc, Each main distribution was installed also with 50Kvar x 12 steps PF capicator with automatic pf controller.
I also noticed another 'abnomal' event , i check some of the motor (new) while start and running at '200A' without load and tripped TOL(dismantle the V-Belt to gearbox) but after start others machines which at the same main switch board and i start again the '200A' motor without load and the running current 35A without load. (The same new motor)
One day the one of the 2500Kva outgoing cables were short to ground ,we pull out all the cable and found cable insulation was harden and crack.
May i know is it of the 'over capacitance' and caused the transformer out going cable insulation failured ? or caused by overloading during the full production running.
Thank you and Best Regards