Dear,
Electrical Earth is the earthing grid made for safety of human . Wherein, the short circuit fault currents are passed into the earth, bypassing current path from operating person's body to the earth. same may protect the electrical equipment thru circuit breakers.
Instrument earth is the earthing system made for improvements in reliability / performance of the electronic instruments / plc systems / computers / digital sensors & process instruments , wherein, the leakage currents of electronic cards/ electromagnetic interferences generated currents / harmonics generated currents & voltages are by passed into the earthing system exclusively made for the instruments & other electronic systems.
Both the earthing systems should be electrically & physically isolated.
Exploring the Science of Electricity
04/06/2009 12:45 AM
Best harry potter,
In your reply the above topic, you comment by saying "Both the earthing systems should be electrically & physically isolated". I can think that is true for instruments having their own power supply, but what if a control unit's control electronics OV are connected to the earth of its own power supply. Doing so, will that not provide a return path for noise and interference?
The best vision is insight - Malcolm Forbes
04/02/2009 10:48 AM
One of the first things you learn working on aircraft, ground ain't ground anymore.
If you do VERY good electrical bonding work, AND making exception for periods of heavy P static; ground will be very close to equal to the negative terminal on the starter battery.
Best you get.