11/15/2006 4:29 PM
Is there any expert on fuses who can explain that gases generated due to circuit interruption process and escape (through the threaded connection of the refill unit) and the upstream breaker trip and recloses. Does the gases generated, escaped and build up around the fuse do they make things worst?
I appreciate your help
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member
Re: Fuse Refill Unit
11/17/2006 3:54 PM
The gasses carry away energy and are part of the proper function of the fuse.
Are you describing a system in which the gasses are used as an indicator to
restore sevice to other unfaulted circuits?
11/17/2006 5:06 PM
As you said, the gases are carry away energy during fault clearing, but my confusion is the padmounted fuse gear burnt. According to the analysis the gas escaped through the loose threaded connection of the refill fuse unit causes this fire, because of the upstream breaker opened and closed on its reclosure scheme. It opened and closed three times, then since there was a gas build up in the fuse cubicle it ignites fire.
What I thought this gas is not flammable or it should not, so I need some explanation thanks for the reply
11/21/2006 11:48 AM
'Indoor` fuses are not supposed to produce flamable gas.
The gas produced can be hot enough to ignite a fire if fuel is present.
Was there any fuel in the enclosure? What burned?
These fuses are supposed to be vented to safely handle the gasses.
You state that the unit was loosely threaded. Did you also check that the
vent was free of obstruction to limit pressure? Are you sure it was not
a failure of the unit due to pressure?
Unless the upstream breaker closed very quickly, the fault should have cleared
before power was restored. Look into the coordination of the fuse and breaker.
If the breaker was opening before the fault cleared it may have prevented the
fuse from clearing completely and thus there was a problem when power was
restored to a damaged but not completely cleared fuse.
11/21/2006 12:39 PM
I appreciate your comment