Anonymous Poster

4-20ma

04/05/2009 5:40 PM

hi all,

as i understand about 4-20ma, for example 4-20ma RPM meter supplyed from analog output module: the volt is variable just to make it for example 12ma for meter half way readings. and it will increase the out put voltage to make it 12ma if the meter was connected away ''longer distance''.

my question is: when we want to test the ma we place ammeter in series with the meter. how about if i want to test the module with ammeter placed direct on the output terminals ''disconnect the meter'', will the module decrease the output voltage and show 12ma for half way reading? or that will be short circuit case as i connect the ammeter direct to the output terminals and the module will detect short circuit ???

hope you got what i mean?

thanks for you cooperations and hope you can supply me with some info!

many thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#1

Re: 4-20ma

04/05/2009 9:26 PM

Dear all,

"when we want to test the ma we place ammeter in series with the meter. how about if i want to test the module with ammeter placed direct on the output terminals ''disconnect the meter'', will the module decrease the output voltage and show 12ma for half way reading?"

You are correct, the module automatically adjust the output voltage and your meter reading is still 12 ma.

"or that will be short circuit case as i connect the ammeter direct to the output terminals and the module will detect short circuit ???"

Even the output is short-circuted, your module will keep the output current 12 ma. The module will not detect the short-circuit, but will work properly. Many 4-20mA modules will work with 0 to 1 or 2kOhms output resistance. So, output can be shorted.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Reply
Anonymous Poster
#4
In reply to #1

Re: 4-20ma

04/06/2009 7:35 PM

hi

thats exactly what i want to know, many thanks for your reply. and also thanks for every body who reply on this forum!

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: 4-20ma

04/05/2009 9:55 PM

These are constant current devices for a wide output resistance range. Hence the amount of output resistance (provided it is within the range) will not affect the reading. BTW: if you directly put the ammeter at the output it is a virtual short circuit isn't it ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: 4-20ma

04/06/2009 1:03 AM

My God people!!!!!!!!!!!!!!!!!!!!

Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#5

Re: 4-20ma

04/07/2009 1:42 AM

Hahaha- My God people.

Speak to me - I am closer :)

Regards,

Craig