DEAR MEMBERS,
WE HAVE A MOTOR, 400V,60HZ,300HP MOTOR, WHAT HAPPENED IF WE SUPPLIED 433V,50HZ. WHAT WILL BE MOTOR PERFORMANCE, IF VOLTAGE IS IN ACCEPTABLE RANGE.
IS ANY PERFORMACE DETORIATE, MAINTENANCE PROBLEMS, ETC.
THANKS
REGARDS
KESHI123
Re: MOTOR SUPPLY
04/06/2009 7:00 AM
<...WHAT WILL BE MOTOR PERFORMANCE...>
  1. Someone will object to the use of Caps Lock
  2. The motor will turn slower
  3. Therefore the cooling fan will not be so effective
  4. If delivering the same torque then it will run hotter, though only the load characteristics can determine this
  5. It will be less efficient
  6. It may have a shorter working life
  7. It will be a poorer choice than selecting the correct motor for the job at hand.
Good Answers: 804
Re: MOTOR SUPPLY
04/06/2009 4:31 PM
GA, you get a vote form me.
  1. Someone will object to the use of Caps Lock... OK, I'll do it. DON'T USE ALL CAPS! It makes it harder to read.
  2. The motor will turn slower... Specifically, 20% slower. However you are also reducing the voltage by 6% and the torque is reduced by the square of the applied voltage, so .942 means you will have 88% of rated torque. But because HP is a function of torque AND speed, the lower speed buys back SOME of the HP. So 20% lower speed, but 12% lower torque still equals lower HP capacity. Your 300HP motor has become a 272HP motor.
  3. Therefore the cooling fan will not be so effective... Check, so lower power capacity, less effective cooling = more heat in the motor = shorter life. For every 10 degree increase in motor operating temperature over rated, the motor winding insulation life is cut in half.
  4. If delivering the same torque then it will run hotter, though only the load characteristics can determine this... Not to be too picky, but what he means is that if the LOAD requires the same amount of torque, the motor will be incapable of delivering it, so the slip will increase, the motor will draw more current to attempt to do the same work (see above) and the extra current will raise the temperature and cause the motor to die sooner than later.
  5. It will be less efficient... Yes, especially if you describe efficiency in relation to being able to perform the job at hand! The motor may not work at all!
  6. It may have a shorter working life... I think that is a given. It WILL have a shorter life.
  7. It will be a poorer choice than selecting the correct motor for the job at hand.... Bingo.
Re: Motor Power Supplies
04/07/2009 3:30 AM
nothing will happen to the motor coz the drive which has attached with the motor posses an error over voltage trip or if the voltages goes hiegher from the range so the voltage depend resistance will burst which is on the input side of the drive n thats all the motor will not damage
NOYHING AS IT SEEMS AS IT APPEARS TO BE