Anonymous Poster

current devider

04/08/2009 5:52 PM

Please help me to resolve our problem

I need source current 4- 20 Ma from level transmitter to control VSD of delivery pump from tank

unfortunetely above source of transmitter has used at DSC control system for controller valve

I can't utilize sorurce of transmitter from DSC because I don't get permited to make addition program to take source Ma from DCS

please give me suggestion how I can find out source MA from transmitter it self with out tuoch of DCS

Regard

Sumardi

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2009
Posts: 227
Good Answers: 11
#1

Re: current devider

04/08/2009 6:47 PM

Hello,

My suggestions are based on the understanding that you already have a 4-20 mA level transmitter that is used to control a valve, you also want to use it to control the speed of a pump motor, but you cannot do anything that interferes with the function of the valve controller.

If your level transmitter has a sufficient supply voltage and your controllers have sufficient common-mode voltage range, you can simply route the signal wire to the valve controller through the VSD input (wire it in series with the valve control input). Both will get the same current.

If, for some reason, electrical modification of the valve control circuit is not permissible, you can use a magnetic current sensor such as the NVE AAV003-10E as the input to another voltage-controlled current source. Information on this part is at

http://www.nve.com/webstore/catalog/product_info.php?cPath=27_28&products_id=544

You would still have to route the signal through the sensor chip, but the small change in impedance should not be significant for what you are doing.

Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#2

Re: current devider

04/08/2009 11:49 PM

I need source current 4- 20 Ma from level transmitter to control VSD of delivery pump from tank

By this, my understanding is that you are trying to control a pump on the outlet of the tank. No control other than 0% level=0% pumping (what happens to the motor at that point?, and 100% level=100% pump capacity? Think about what will happen to the downstream process.

I presume that DSC (no idea in this context) and DCS (Distributed Control System) are the same?

I can't utilize sorurce of transmitter from DSC because I don't get permited to make addition program to take source Ma from DCS

From that, and the next line, tells me that someone else has control of the programming. Talk to those people. If the concept is valid, you should be able to convince them that the additional programming is worthwhile. Since you have a VSD, there is no reason it could/should not be controlled. But it has to be controlled in such a way that it does not hurt the downstream process.

If there are no objections, then a I/I (current to current converter), can be installed that will supply both the DCS, and your circuit.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Reply
Participant

Join Date: Mar 2009
Location: I am citizen of Canada but now stay in Iran
Posts: 4
#3

Re: current devider

04/09/2009 11:11 AM

Hi

I think you can use rosemont transmitter or:

Use the electromecanical level controll with a sensor and pump you can use this with bypass link.

Reply Off Topic (Score 5)
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#4

Re: current devider

04/10/2009 1:00 AM

Use an isolator that gives two outputs...

there are a good amount of vendors who manufacture these.

Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#5
In reply to #4

Re: current devider

04/10/2009 1:09 AM

http://www.pepperlfuchs.com/products/product.jsp?product_id=18381 MODEL : KFD2-STC4-EX1.2O This will act as an isolator for field transmitter and provides two isolated 4-20mA outputs

Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#6

Re: current devider

04/10/2009 1:10 AM

http://www.pepperlfuchs.com/products/product.jsp?product_id=18381 MODEL : KFD2-STC4-EX1.2O This will act as an isolator for field transmitter and provides two isolated 4-20mA outputs

Reply
Active Contributor
South Africa - Member - Automation & Control Engineer

Join Date: Mar 2009
Location: Mandeni, South Africa
Posts: 13
Good Answers: 2
#7

Re: current devider

04/10/2009 2:02 PM

hi,

you really need to get this signal from your DCS where you can implement PID control or something similar over the VSD. By using the ma source of the transmitter direct to the VSD (bypassing the DCS) makes it a hidden function which when it goes wrong no one will know about. On the DCS you will have graphics, trends and diagnostics.

Convince the programmers that this is the way to go. I am a DCS programmer and i wouldn't refuse this request. This is what the DCS is for.

__________________
Regards, Dave
Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#8

Re: current devider

04/13/2009 4:03 PM

hi, sumardi

what you need for vfd drive, is not only lvl xmtr signal but also a controller and a isolator in this condition campare with the dcs requirements ie; one output in dcs and isolator /barrier to connect to vfd so make a comparison with this two options and added features of with dcs ie ;auto/manual station,alarm , trend and diagonistic features .Finally campare with time and cost for installation.

Select what is best to process .

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

davegr (1); find2am (1); Kilowatt0 (1); MNIce (1); naveen_menon (3); raybaxi (1)