Current unbalance in VFD drive by G5 yaskawa.

04/11/2009 2:43 AM

Dear Sirs,
we have installed 18.5 kw vfd drive and we have observed that cureent pahses are at no load 4.6amp,4.8amp and 3.1amp. But resistance is balance in all three phases and insulation level is also high. This is only one example i am citing here.In general all the vfds installed here are showing this type of unbalancing of current.
i will be pleased to know why is it happenenig?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Sep 2008
Location: Rourkela,Orissa,India
Posts: 19
#1

Re: Current unbalance in VFD drive by G5 yaskawa.

04/11/2009 8:36 AM

The reason may be the unbalanced voltage between 3 phase of your supply system.

Register to Reply
Member

Join Date: Feb 2009
Posts: 8
#2
In reply to #1

Re: Current unbalance in VFD drive by G5 yaskawa.

04/11/2009 8:47 AM

voltage in supply system is balanced and it is 409v,410v,404v.

Register to Reply
Active Contributor

Join Date: Feb 2009
Posts: 22
#3

Re: Current unbalance in VFD drive by G5 yaskawa.

04/12/2009 5:01 AM

is it new motor or rewound motor?.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4

Re: Current unbalance in VFD drive by G5 yaskawa.

04/12/2009 11:23 AM

At low load, the 4-6V of voltage imbalance that you have is enough to produce a small current imbalance. ~1A imbalance is negligible on a approx 20A drive. Don't worry about it unless it reaches 5-10A at full load. If it does, look for the reasons for the line voltage imbalance. The drive is not likely to be the cause for the current imbalance. The line voltage imbalance is more likely it.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Anonymous Poster
#5

Re: Current unbalance in VFD drive by G5 yaskawa.

04/13/2009 11:20 AM

u must check the incomming supply voltage

if it is unbalanced

Register to Reply
Anonymous Poster
#6

Re: Current unbalance in VFD drive by G5 yaskawa.

04/13/2009 1:16 PM

Voltage at source can differ from voltage in motor winding due to resistance in the supply circuit cable terminations. This could cause a difference in current values.

Register to Reply
Anonymous Poster
#7

Re: Current unbalance in VFD drive by G5 yaskawa.

05/10/2009 4:36 PM

please check the incoming voltage if it is balance, considering that the motor have balance resistance and high insulation in all three (3) phases. If it is found unbalance, expectedly the current will have too.

Register to Reply