Previous in Forum: Current unbalance in VFD drive by G5 yaskawa.   Next in Forum: Sourcing Flowmeters
Close
Close
Close
6 comments
Rate Comments: Nested
Active Contributor

Join Date: Sep 2008
Posts: 13

residence time

04/12/2009 2:12 AM

dear all

I am preparing a duty spec for new instrumnet air package system. this package will comprising air compressor, air drier, and air receiver. this package will be just appropriated instrument air supply. on the other hand plant air supply is not in scope of work of this package.

based on this explanation, I want to specify size of instrumnet air receiver based on required flow rate, lower and upper pressure, and residense time. two above mentioned items are known for me. but I don't know about minimum residense time.

my colleague says that I should take residense time of instrumnet air resevoir equal to 3 min. but I want to know is there any figure in ISA standard in this regard?

thanx

Hossein

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor
Engineering Fields - Control Engineering - Automation Engineer Egypt - Member - Mohamed Salaheldin

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 18
#1

Re: residence time

04/13/2009 12:56 AM

Did you revise ISA standard (ISA - 7.1.01-1996 Quality Standard for Instrument Air). It may be useful??

Register to Reply
Active Contributor

Join Date: Sep 2008
Posts: 13
#2
In reply to #1

Re: residence time

04/13/2009 1:47 AM

I perused this standard and I could not find any figure about my request in it

Register to Reply
Associate

Join Date: May 2008
Location: Seoul, Korea
Posts: 35
Good Answers: 1
#3

Re: residence time

04/13/2009 2:43 AM

Taking the definition of Residence time as surplus air supply duration (maintain the air pressure between upper & lower pressure) even when the air compressor fails to operate by any reason.

Such requirement may not be appreared in standard including ISA since it is not the standard requirement. It is specific requirement as I believe.

Since the air pressure in air receiver is not always maintained at upper pressure, the same air receiver can durate various residence time.

I would recommend you to take Min. 5 min. for residence time based on my experience, whatever specified in the specification of the plant. Sometime, 3 min is not sufficient to control all air-operated instruments since some of them are relayed several mins by the logic.

Hope it will help you!!

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#4

Re: residence time

04/13/2009 9:24 AM

I'm not aware of any standard governing this.

There are two questions I would ask myself here:

  1. How long does it take my redundant air compressor to come online (if you have one)? That will set my bottle size and then I would add some buffer.
  2. How long does it take an operator to go out there and give it the 'ole restart try? Again, this time lag will set the bottle size and then add some buffer.

Sometimes, you have a system that will interlock on instrument air pressure (in my experience, a PSA system had a low IA pressure interlock) that may also affect receiver sizing.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#5

Re: residence time

04/14/2009 12:54 AM
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#6
In reply to #5

Re: residence time

04/14/2009 9:09 AM

Neat article, thanks for the link!

__________________
Money doesn't talk, it screams in your face.