Fire Suppression Nozzles and Orifice Diameter

04/15/2009 4:06 AM

Dear Friends,

Our vendor supplied Automatic Fire Suppression System on the HFC227es based(NFPA 2001) . As per there hydraulic calculation ,they suplied most of the materials with gas(HFC227ea). But when they installed there equipments I have noticed there are no orifice on the nozzle , asked them the said they are localy drilled and make orifice diameter . is it ok for us , as per my knowledge , manufacture prepare there hydraulic calulation and drilled and made orifice diameter. If they localy make , which part is importad to rectify.

Extingusher Gas: HFC227ea

Design Concentration( A,B,C,D & E type fire): 7.2%

Working Pressure: 25bar

Number of Zone: 3 (Three)

FCP: COnventional (Cross Zone type)

Register to Reply
Pathfinder Tags: Oriface Diamer of Nozzle
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Jan 2009
Location: Houston, TX
Posts: 54
#1

Re: Fire Suppression Nozzles and Orifice Diameter

04/16/2009 10:56 AM

We have had some fire suppression systems installed on our grinders, and we have never had to drill any type of hole.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Fire Suppression Nozzles and Orifice Diameter

04/16/2009 12:32 PM

No it is not ok for them to do that. I am a fire protection engineer who has been designing these types of systems for 30 years. I have worked with virtually every manufacturer of this type of equipment, which is highly regulated due to the liability imposed by misuse. They are allowed to hydraulically calculate the system for pipe and nozzle orifice sizing using the manufacturer specific software. That software will be licensed to them only if they prove to be competent. The nozzle orifices are selected by the software, and custom drilled to order BY THE MANUFACTURER. The nozzles are UL Listed and Factory Mutual approved, The installer cannot drill them. If they have done that, your system carries no warranty, no listing, does not meet any code, and will not be backed by the manufacturer if it fails to put out a fire.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2009
Location: Dhaka, Bangladesh
Posts: 11
#3
In reply to #2

Re: Fire Suppression Nozzles and Orifice Diameter

04/18/2009 5:55 AM

Dear WJMFIRE,

I have collected NFPA 2001 and NFPA 70 book, please give any any more information which is match your openion that books article or page no. I am agree with you, they have NFPA certified engineer , he said it is does not matter in locally drilled or manufacture drilled , main thing is it implementation according to the NFPA guideline(they emphasis there are openion ).

I am not expert in this fields, that why I haven't sifficient information.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#4
In reply to #3

Re: Fire Suppression Nozzles and Orifice Diameter

04/20/2009 3:12 PM

NFPA 2001 clearly states that discharge nozzles must be "Listed". This means the organization who drills the orifice must be a UL Listed or Factory Mutual (or some other listing laboratory) approved manufacturer. Ask them to produce this documentation. Also, NFPA states that "discharge nozzles shall be permanently marked to identify the manufacturer as well as the type and size of the orifice". These nozzles do not appear to meet this section of the Code.

Also, for the record, I am a longtime member of NFPA. I assure you that NFPA will not certify anyone. The only organization who will certify an individual as to their knowledge in this field is NICET.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Register to Reply 4 comments