Heat load calculation for transformers

04/15/2009 10:31 AM

How can you calculate transformer heat load for A/C sizing

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#1

Re: Heat load calculation for transformers

04/16/2009 5:57 AM

Hi,

As a rule of thumb the heat dissipation will be a function of the MCR ( Maximum Continuous Rating) and the overall efficiency of 98% at a pf of 0.98. This will suggest something in the order of 2kW per 100kW load. There is a manufcturers' losses curve usually available for these products.

You should remember that there remains a standing loss value even if the transformer is completely idle as this represents the iron loss.

It is a pity to see A/C being used to cool a transformer as you will have to add these incurred parasitic losses to the inefficiencies of the installation. Also remember what will happen when the A/C unit falls over do you have to add a stand-by unit just in case? Far better to have the beast naturally cooled all round and avoid all these added life time costs and additional maintenance liabilities.

hope all goes well.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Reply
Participant

Join Date: Sep 2012
Posts: 1
#2
In reply to #1

Re: Heat load calculation for transformers

09/18/2012 11:08 AM

Ok I have a issue figuring out the heat load for some transformers, Their 12470 to 4160 V the 4160 has an amp rating of 270 and the 12470 amp rating is 123. Some help with this calculation would be helpful.