What should the air gap be on a 15KV (3000A) vertical bus for switchgear ? insulated / uninsulated
Re: Air gap
04/16/2009 5:58 AM
Starting the ball rolling:
  • Given that the insulation breakdown voltage in dry air at ambient temperatures and pressures is about 30kV/cm, the absolute minimum it could ever be for uninsulated conductors is 5mm, and will in practice be considerably more.
Good Answers: 27
Re: Air Gap - Vertical Bus for Switchgear
04/17/2009 9:34 AM
It depends upon the air gap and electrode geometry (rod or sphere) and the application altitude above sea level. Standard 1/2" rod and sphere gap spacing for alternating and impulse voltages, as well as the appropriate correction factors, are included in IEEE Std 4 (ANSI C68.1).
04/17/2009 10:26 AM
When I worked in medium voltage switchgear, we actually used a combination of air gap and epoxy coating to insulate the phases from each other and from ground. Of course the thickness of the epoxy affected the amount of air gap required, and visa versa.