whose accuracy is more measuring or protection CT

04/17/2009 1:20 PM

Please explain in details.and give some authors and book name to study it in detail.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#1

Re: whose accuracy is more measuring or protection CT

04/17/2009 2:29 PM

Sounds like a homework question. I'd suggest doing some Google research first, then asking specific questions.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: whose accuracy is more measuring or protection CT

04/17/2009 5:20 PM

Definitely the measuring CT has to be more accurate.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Participant

Join Date: Nov 2008
Posts: 2
#5
In reply to #1

Re: whose accuracy is more measuring or protection CT

05/03/2009 6:12 AM

Sir here i had ask qustion not suggestion so if u knw answer then reply ,rather than suggesting ,google because it is a search engine its answer's more than needed,i needed specific answer and reason.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: whose accuracy is more measuring or protection CT

04/18/2009 3:36 AM

Measuring ct is more accurate.

Class 0.5 ...... 0.5% accuracy

Class 1........ 1% accuracy.

Protaction cts need not be that accurate, but should not saturate at the short circuit levels.

So,

Class 5P10 ....... 5% accuracy, but 10*Ir fault levels can be sensed without saturation

Class 5P15 ........ 5% accuracy, but can handle 15* Ir fault level.

__________________
Exploring the Science of Electricity
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: whose accuracy is more measuring or protection CT

04/20/2009 2:34 AM

Class 5P20 ...... 5% accuracy at 20*Ir fault leves, (and 1% at rated current).

Class 10P20..... 10% accurracy at 20*Ir fault leves, (and 3% at rated current).