UNBALANCED LOAD READINGS FROM A SET OF 33KV CURRENT TRANSFORMERS

04/18/2009 12:01 PM

I want to find out what could be responsible for the imbalance in the loading of the metering core of a set of 33KV current transformers.I obtained a balanced reading at the CT terminal box but an unbalanced reading at the control board(downstream,close to the load).The load on this core is an energy meter and an ammeter. However the readings on the protection core is balanced.As a temporary measure, I have shorted out the metering core pending when I get solution to this problem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: UNBALANCED LOAD READINGS FROM A SET OF 33KV CURRENT TRANSFORMERS

04/21/2009 9:06 AM

Usually an imbalance at one end but not the other means that something is wrong with the metering equipment at one end. Logically it would be the end where the imbalance is being detected.

To test this theory, you need to re-arrange the metering core by transferring them to a different phase, or reattach the lines to the loads while maintaining the correct phase direction. If the core is defective, the problem will follow the defective transformer. If the load is truly imbalanced, it will yield the same readings for each of the respective phases.

The end that measures a balanced load is very unlikely to have exactly the right defect to correct for an imbalanced load. But it is still slightly possible. Check both ends after you make the changes to see what shows up. You will be looking for what changed and how it changed with respect to what you did to change it.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle