Anonymous Poster

overheating transformer rectifier

04/20/2009 4:20 AM

Hi all electrical engineers

We have a transformer rectifier unit (TR) about 20 years old powering an electro chlorinator unit. Original Spec was 1500A at 30V. As part of a plant refurbishment project this unit was sent away to local specialists for refurbishment and was returned to site about 2 years ago. It was reconnected to the power supply 6 months ago and demonstrated that it switched on and delivered power but was not fully tested. Recently we have tried to commission the plant but have found that the rectifier section overheats causing the plant to shutdown. The diodes appeared to be drawing different currents and on the specialists recommendation all diodes were changed. Now we have run it without causing a temperature trip at 26V / 1300A with a side cover removed to allow temperatures to be measured and obviously better airflow over the heatsink. On repeating the run with the side cover in place it tripped after just over one hour and it is obvious from the temperature measurements that the first run was on the limit. Can anyone tell me what might be the cause in a unit which we understand was able to deliver the specified current before it went away for refurb. The transformer section appears to be running cool. I am not an electrical engineer but would like to be able to ask the supplier some informed questions.

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Australia - Member - Igor...pull the switch!!!

Join Date: Apr 2009
Location: Australia, sunny North Queensland
Posts: 380
Good Answers: 12
#1

Re: overheating transformer rectifier

04/20/2009 5:35 AM

Assuming the rectifiers/diodes that were replaced on the advice of the specialist's recommendation are not under rated for their given task, I (and others at a guess) would like to know what was involved in the initial refurbishment two years ago.

I would guess that on some occasions, the replacement of old rectifiers/diodes with their more modern counterparts may require a more efficient (larger?) heat sink and new suitable fan, possibly demonstrated by the fact that an improvement in air flow reduced the likelihood of failure caused by heat.

Were other components "updated"?

__________________
CraziestOzzy
Reply
Commentator

Join Date: Oct 2008
Location: Gaborone, Botswana
Posts: 89
Good Answers: 22
#2
In reply to #1

Re: overheating transformer rectifier

04/20/2009 6:09 AM

Thanks for the comments. I am waiting to get confirmation of the refurbishment but I believe the main change was a new control circuit board and a general cleanup. There is no cooling fan, it relies on passive cooling. We are thinking that this will be the way to go as it would be relatively easy to add some fans. May be you are right and the new diodes need a better heat sink and the overheating before we changed them was due to faulty old diodes.

__________________
johnbots
Reply
Power-User
Australia - Member - Igor...pull the switch!!!

Join Date: Apr 2009
Location: Australia, sunny North Queensland
Posts: 380
Good Answers: 12
#3
In reply to #2

Re: overheating transformer rectifier

04/20/2009 6:18 AM

Twenty year old diodes replaced for more modern ones (without knowing the details of the component) would generally on some occasion require a suited heat sink for that particular diode...the specs for heat dissipation are usually specified inside the manufacturer's datasheet. You can never go wrong with fans.

Would be interesting to see what confirmation you get as far as the refurbishment is concerned. A new for old circuit board would in my opinion not be the cause of your current problem, unless something was incorrectly done there, but very doubtful on that point.

Cheers

__________________
CraziestOzzy
Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#4

Re: overheating transformer rectifier

04/20/2009 6:45 AM

Dear,

following may be the causes....

1. Chexk for any modifications done while refurbishment. This may be obstructing the natural cooling. I had experienced even with the layer of varnish poured on it.

2. Check for the quality of diode soldering. End terminal connections. If they are not proper, diode may be heated up , keeping transformer cool.

Even defect in your external connections lead to the similar problem. this nothing but the generation of 3rd harmonics in diode area.

3. Check for the proper installation of new diodes with correct confirmed diode rating with size of heat sink.

__________________
Exploring the Science of Electricity
Reply Score 1 for Good Answer
6
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5

Re: overheating transformer rectifier

04/20/2009 11:48 PM

in a high current unit like this you need to eliminate anything that impedes the voltage path and the heat path. Remember wattage = IxIxR, where I = 1300 amps, so any connection must be either a properly soldered connection or a gas tight connection between bright conducting metal tightly done. In the heat path, the diodes are either threaded into a heat sink or made to bolt with a flat surface against the heat sink. Ideally this will be a bridge rectifier with each heat sink floating so that the diode can make perfectly flat metal to metal contact with the heat sink and has the proper high thermal conductivity heat transfer medium squeezed to the proper thin section.

Another aspect. It is probable that they used Shottky diodes in the initial design. These have only .3 volt forward drop versus common dioes that have a .7 volt forward drop. I say probable, as this low drop increases efficiency, and reduces the wasted heat.

So check on those aspects, if you can find the original diodes, hey are easy to test, just run 10 amps through them with a resistor to limit the current (1 ohm 200 watts for a 12 volt battery = 12 amps ccurrent), then measure the voltage drop across the diode when current is flowing (backwards = no current = the blocked ddirection). It will be either just under 1 volt or just under .5 volts. If you have a good voltmeter, .7 or .3 volts forward drop.

If the experts used common high current silicon diodes with .7 and should have used shotky diodes, there is the problem. Shotky diodes are a lot more expensive than cheap silicon diodes, someone who wants to maximize profits of does not know his nether aperture from a mole's home might be involved??

These flaws are speculation, but it does give you some things to look at.

__________________
Per Ardua Ad Astra
Reply Good Answer (Score 6)
Commentator

Join Date: Oct 2008
Location: Gaborone, Botswana
Posts: 89
Good Answers: 22
#6
In reply to #5

Re: overheating transformer rectifier

04/21/2009 1:06 AM

Thanks Aurizon for a very comprehensive reply - I have the old diodes so will be able to test them. We are meeting the experts today so should be able to determine their awareness wrt their fundamental orifice!

__________________
johnbots
Reply
Power-User

Join Date: Jan 2007
Location: Berlin (Germany)
Posts: 332
Good Answers: 1
#7

Re: overheating transformer rectifier

04/21/2009 6:33 AM

Hi,

I think you possibly use a diode array of paralleled diodes. If so, there might be a problem with the temperature coefficient (delta Uf/delta T). If they used diodes with a negative tempco there may be a runaway problem of the "best" diode which has the lowest Uf, carries the largest current, lowers the Uf, carries more current, gets hotter, lowers the Uf, +I, +T, -Uf, ... and so on. Overheating is pre programmed then.

Regards Uwe

__________________
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#8

Re: overheating transformer rectifier

04/21/2009 9:24 AM

Could it be that the unit was never fully load tested at 1500 A at 30 V?

At that current , each diode will dissipate 910 watts ( with a forward diode voltage of 0.7V). How many diodes do you have?

From your post you suuggest that with the cover off, the unit is marginally below the temperature limit. My guess would be that the units was never able to meet the full load unless the physical area around the control box was chaged significantly to prevent free air circulation or increase the ambient temperature.

From past experience , I have run into similiar situations where the operators report that a particular item of plant is not achieveing full output only to realize that it never did.

Another situation , with a battery charger, was traced to a root cause of an HVAC unit hot air discharge increasing the general ambient temperature in the area of the battery charger limiting the current. The HVAC unit was installed while the machine was down for a 3 month major overhaul.

__________________
Learn more, Do more , Be more
Reply
Commentator

Join Date: Oct 2008
Location: Gaborone, Botswana
Posts: 89
Good Answers: 22
#9
In reply to #8

Re: overheating transformer rectifier

04/21/2009 10:37 AM

Thanks djacob for your comments.

I suspect that you are right that it never achieved the specified output but we have no way of proving it. This unit was made in the UK but has been in Southern Africa for its working life with significantly higher ambient temperatures and lower maintenance & monitoring!

One factor which I only learnt this morning was that the aluminium heatsink and diodes appear to have been laquered during the refurbishment with a 'copper' coloured resin. I am not sure why this was done or if it is normal practice but it strikes me as being one major modification which would affect heat dissipation.

A factor which we see here is where a makeshift or mistaken 'repair procedure' at some in the past becomes the 'norm' from then on so that equipment remains in the wrong condition for ever more. In this case something as simple as replacing the side covers the wrong way up would move two of the air vents to a less effective position but it can be difficult to persuade anyone to change it because that's 'how it has always been'.

Thanks to all for your comments.

__________________
johnbots
Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#10
In reply to #9

Re: overheating transformer rectifier

04/21/2009 10:55 AM

Since this unit was made in the UK over 20 years ago, I may not in fact have Shottky diodes. It may use the standard silicon ones.

It may be a good idea to add a ball bearing blower to the heat sink box.

I am not sure what the copper colored varnish was. Ask them what merit such a varnish could have?

__________________
Per Ardua Ad Astra
Reply
Associate

Join Date: May 2007
Location: Riverdale, Utah USA about 30 miles north of Salt Lake City
Posts: 29
Good Answers: 3
#11
In reply to #9

Re: overheating transformer rectifier

04/25/2009 4:05 AM

I would be very suspicious of ANY resin, paint, etc., applied to a heat sink. Of course, if it is a specialized treatment which only looks like resin, designed to improve heat dissipation, that is different. I have seen some very poor heat sinks in low power situations which were marginally improved by being "painted" black with high temperature paint, but I doubt it would be the same for such high power diodes.

I would very thoroughly and suspiciously question the use of the material on the heat sink, especially if it is any kind of paint, plastic/resin, etc. , and especially, if it is very thick. What material is used for the heat sinks? Is it the same material used in the older design, or perhaps even the same heat sinks?

__________________
kosimov
Reply
Commentator

Join Date: Oct 2008
Location: Gaborone, Botswana
Posts: 89
Good Answers: 22
#12
In reply to #11

Re: overheating transformer rectifier

04/25/2009 5:09 AM

Thanks Kosimov for your response. The resin appears to be simply a sealant against water or damp. I am waiting for confirmation whether it was applied during the refurbishment or was original. I also doubt that it adds anything to the heat dissipation. It is also the one factor which appears to have changed which could account for the decrease in performance. The heat sink is aluminium and is the original. The problem is that it will prove difficult (and expensive in time and money to correct this)

Will keep you all posted on further developments. Thanks again

__________________
johnbots
Reply
Reply to Forum Thread 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aurizon (2); CraziestOzzy (2); djacob (1); harry potter (1); johnbots (4); kosimov (1); uweka (1)

Previous in Forum: Galvanic isoltion   Next in Forum: Formula for Online tan delta

Advertisement