plc battery checking

04/20/2009 6:23 PM

i would like to know how to check plc battery validity..

also i want to know how to install it and what is the limitation during replacement?

how can i check for it before problem occurs to avoid production stoppage.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: plc battery checking

04/20/2009 10:38 PM

There is no way to check the PLC battery validity. The only things that you can do, is to record the date and time, when you last replace the battery. The battery need to be replace within every 2 years.

When you replace the PLC battery, you got to do it while the PLC is power up otherwise you will loss all the program if you replace the PLC battery with power shut down.

As long as the power supply is "ON" your PLC will be working fine without the battery. But don't take the risk.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2008
Posts: 24
#3
In reply to #1

Re: plc battery checking

04/21/2009 12:31 PM

thanks for your reply.

can u send me a link that give more elaboration about plc hardware ,internal strucure, the common preventive maintenance for plc?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: plc battery checking

04/21/2009 3:12 AM

Simply place the battery on planned preventative maintenance schedules.

  • Ooooh! How about running a timer within the code that starts when a new battery is installed, and when expired in, say, 2 years raises an alarm on the human-machine interface?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#4

Re: plc battery checking

04/21/2009 11:36 PM

Just had a customer find out after he shut down a production machine for 3 months (slowdown in sales). When he did try to start it up no go!

Battery dead, plc lost the whole program!

We were able to locate a backup copy (5 1/4 floppy drive) with some version of the machine program on it, but to find Modicom 984 programinng software and a Windows 98 or earlier laptop took some work.

Program has been installed and debug being done this week. The boss was P.O.'d to no end because a $12.00 battery was not replaced! You want to be sure to replace the battery every 2-3 years. Think of how long your laptop battery preforms and you get the idea.

Software, legacy laptops, cables, current machine programs etc. are also things to have on hand. Good Luck

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5
In reply to #4

Re: plc battery checking

04/21/2009 11:55 PM

That too bad. The person incharge should know better what is the procedure to be taken during the plant shut down.

We also had plant shut down for a few month but the power supply still maintain to all the PLC and other control equipment. We always backup all the PLC programs every month for the latest version available.

The battery inside the PLC is use to help you to maintain the PLC program, if there is some power failure, that last for a few hours. It does not help you to maintain the PLC program for 3 month long. No battery can stand for that long period.

Some of the PLC program are store inside the RAM so that we can do some modification on the programs on line. RAM need battery to be back up all the time for the program.

Of course, you can program all your PLC program in to your Eprom but if you do so, you cannot change or modified any program on line.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Anonymous Poster
#6

Re: plc battery checking

04/22/2009 2:23 AM

It is depend on manufacturer .In catalogs manufacturer explain about life of battery. You do not mention a manufacture of your PLC. If your PLC is Siemens that you just on power of PLC remove old battery and insert new one. Life of battery is 3 to 5 years.

Register to Reply
Anonymous Poster
#7

Re: plc battery checking

04/22/2009 4:37 AM

On most PLC's I've ever worked on, there's normally a battery alarm indicator on the CPU. Also there's also an internal bit that turns on when this indicator is on. From this you could bring up an alarm on your HMI (if you have one), or to an output and an external indicator, to inform you the battery needs replacing.

Even if you have a new battery, with all power off, they will probably last no more than 3 months anyway.

Register to Reply
Anonymous Poster
#8

Re: plc battery checking

04/22/2009 4:43 AM

hi ,

some PLC have one Indication light (Siemens ) when Battery is low he lit up . Othr wise you check Battery voltage. some time voltage show is ok but when you battery insert in plc it is not work. so you battery out & check battery voltage on load & this time voltage measure if voltage dropp so battery change. When you replace the PLC battery, you sure PLC is power up otherwise you will loss all the program if you replace the PLC battery with power shut down.

As long as the power supply is "ON" your PLC will be working fine without the battery. But don't take the risk.

Register to Reply
Power-User

Join Date: Jan 2008
Location: Toronto, Canada
Posts: 302
Good Answers: 4
#9

Re: plc battery checking

04/22/2009 11:47 AM

I'll have to say locate and read the PLC maintenance manual.

__________________
Pineapple
Register to Reply
Anonymous Poster
#10

Re: plc battery checking

04/23/2009 6:43 PM

As you propably know modern plc´s like Modicon M340 has no battery.

some older plc´s with batteries for their internal memory can also start up the program from a memory card even if they have a broken battery and the power goes of. But some of the older memory cards also have battery that needs to replace.

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#11

Re: plc battery checking

04/23/2009 7:37 PM

The RSLogix 5000's that we use have an indicator on the plc controller card and we have that sync'd to an output to the HMI as well. We also have replaced the standard batteries with larger external ones. For extended shutdowns we ensure the the plc has 120vac supplied to prevent programming loss.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Participant

Join Date: Jun 2009
Posts: 1
#12

Re: plc battery checking

06/25/2009 3:08 PM

Guys, as for PLC battery replacements, there is a good selection at this spot:

www.batterytex.com

I've used them a few times...the Comp-239 (br-e5c5a) from Panasonic was priced well for me...


-Trev

Register to Reply Off Topic (Score 5)
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); MIKE L. (1); noshorts (1); Pineapple (1); PWSlack (1); ramydiab (1); Simon Wan (2); Trevor22 (1)

Previous in Forum: Diagram for Mitsubishi Pinni Model H66WMNJ6IA   Next in Forum: Auto Reclosing brakers
You might be interested in: Check Valves, Battery Holders

Advertisement