I have a situation on 33kV where the current needed for the circuit is easily satisfied by a 50mm squ. 3 core cable but because of the 40kA for 1 sec. fault level on the system it's fed by I'm being forced to oversize the cable by far. Do I just take the fault level as given by cable manufacturers (AS, IEC etc.) and spec. it accordingly or should I consider time in the fault by the breaker limiting the fault level, i.e. best time is eg. 0.1 sec hence the "let through energy" is I*I*t (fault current squared multiplied by time) compared to the equivalent of the energy the cable can handle? If so do I use RMS fault current or Peak fault current?