04/29/2009 12:44 PM

whts the difference b/w Class X CT and class PX CT?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: Protection Class CT's

05/02/2009 9:00 AM

dear,

Instrument class CTs read Calss X as X% accuracy

Protection class CTs read Calss XP Y , X = % accuracy, Y = Y* Ir.( i.e. Y times the current fault level then the rated value , CT does not saturate, & relay trips the breaker reliably )

__________________
Exploring the Science of Electricity
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Protection Class CT's

06/11/2009 1:07 AM

sir

can u give me chat of the diffent ct use for the protection