Ask the manufacturer. If you can't get anywhere that way, look at data for transformers of similar size & construction for which you can find the data, and take the average (or lowest, if you want to be on the safe side).
__________________
"Love justice, you who rule the world" - Dante Alighieri
You need all these information to do the primary current calculation.
__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
I don't know the power (KVA), The primary voltage is 415V, Secondary Voltages are 24V 2.5Amps, 24.5V 5Amps, 220V 2.5Amps I know only these informations from my transformer.
Assume 80% efficiency, so input is ≈ 912VA. That gives input current ≈ 912/415 ≈ 2.2A. (Primary current = KVA/V)