Air Conditioners: Is the Compressor Too Big?

04/30/2009 9:26 AM

Is it OK to use a 2 ton Compressor/condenser with a 1.5 ton air handler [evaporator coil] if you add an expansion valve and slow down the fan speed?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#1

Re: Air Conditioners: Is the compressor to big?

04/30/2009 9:55 AM

Hello Dan:

In short no, you're going the wrong way, you could probably get away with the combination utilizing an expansion valve, although it likely would be inefficient. If anything you need to exchange more air through the evaporator so a higher fan speed would be beneficial.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply
Associate

Join Date: May 2007
Posts: 45
#2

Re: Air Conditioners: Is the Compressor Too Big?

05/01/2009 3:08 AM

I assume that the compressor is not an open type but a sealed unit (hermetic) type. In which case it requires a certail amount of cold refrigerant to cool the motor windings. When the imbalance is, as you suggest, without a TX valve, you will incrfease the superheat of the returning refrigerant beyond 11 deg F and the electric motor windings will overheat. A TX valve will control superheat. As the imballance is in this case minor you will probably get away with it. If you have iceing problems with your evaporator, you can correct this by using a crankcase pressure regulating valve or an evaporatot pressure regulating valve assuming that the evaporator air quantity is at it's peak.

Good luck

Phill

Register to Reply
Associate

Join Date: Apr 2009
Location: Kansas USA
Posts: 47
Good Answers: 7
#3

Re: Air Conditioners: Is the Compressor Too Big?

05/01/2009 11:57 AM

You need to check btu ratings on all items in the system.
In the past many condensing units were rated as 2 ton
but had a 1 1/2 ton compressor to claim better efficiency ratings
but they had to have a 2 ton cooling coil and 2 tons on air flow
to get 2 ton performance
If you actually have a 2 ton condensor w 1 1/2 compressor w a 1 1/2 coil

It should work
Some compressor mfgs took tons/hp out of their model numbers and show btu rating

I always try to get enough air flow to get 20 degree drop across the cooling coil
72 in 52 out but sometimes the system just won't do it with low air flows

USA Mfgs suggest on a/cs 400 cfm per ton or coil defrosting will be your next problem

Cheating on coil sizes causes higher td's and higher electric bills
Adding back pressure regulators will stop frosting but adds more pressure drop

Why give it to the electric company?
JR

Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#4

Re: Air Conditioners: Is the Compressor Too Big?

05/01/2009 2:28 PM

If I understand you. You wish to use a 2 ton condensing unit with a 1.5 ton evaporator/ air handler. It will sort of work, but not very well. You will have problems with the suction/ vapor return line vapor pressure. It Will not be efficient and it will not last long.

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Icarus (1); jgroberson (1); philiplyon (1); YWROADRUNNER (1)

Previous in Forum: Greener Photography   Next in Forum: Replacement of Transite (Asbestos Cement) Siding
You might be interested in: Power Conditioners

Advertisement