Cable Sizing

05/03/2009 1:17 AM

What should be the Cable Size for the following load?

total power =223 kw

I = 400 A

V = 400 Volt

IK = 120 KA

Distance = 200 meters

please advice

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Cable Sizing

05/03/2009 12:40 PM

Dear Guest,

For deriving required cable size, we have to calculate the allowable voltage drop at starting and running conditions. For that, we need to know the type of load including the power factor, the Switch Inrush current, etc.

Once these data are available, we can derive the cable size keeping in view of allowable voltage drop by using proper resistance/reactance values of various cable sizes and the length of the cable.

regards,

Hitesh Shah

OMAN

Reply
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Cable Sizing

05/03/2009 3:23 PM

please advice

If this is homework, do it yourself. If this is for a job get a professional to do it as you do not appear to be qualified.

__________________
jack of all trades
Reply Good Answer (Score 3)
Associate

Join Date: Mar 2009
Location: Ras Al Kaimah
Posts: 44
Good Answers: 1
#3
In reply to #2

Re: Cable Sizing

05/03/2009 5:25 PM

you are much wisdom jack of all trades. youcatch lazy people. you get GA.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Cable Sizing

05/03/2009 7:13 PM

Look in you local code book for a cable with 400 amp ampacity. You information is not correct. 223 kw at 400 volts does not = 400 amps. info missing?

Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5
In reply to #4

Re: Cable Sizing

05/04/2009 3:03 AM

Even Ik = 120 KA seems mis leading. for such a small feeder, Ik should not be more then 15 KA. max. in any ways.

__________________
Exploring the Science of Electricity
Reply
Anonymous Poster
#6

Re: Cable Sizing

05/09/2009 12:24 AM

223kw at 400 volt 3 phase=185 amp for 200 meter lenght using cable size 120 mm sq

pvc xlpe cable size

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

agila (1); Anonymous Poster (2); harry potter (1); jack of all trades (1); wareagle (1)