installed power vs transformer rating

05/03/2009 3:22 AM

For one of the residential building the installed power is working out around 190 kw for all the units including for AC's.I appreciate if somebody can suggest suitable rating for the transformer to be installed and also how to take care of overloading.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: installed power vs transformer rating

05/03/2009 3:35 PM

Size the transformer for the intended load (including any estimated new loads due to expansion, etc), peak motor and compressor load, environmental de-rating (such as high ambient temperature, you could be in Dubai for all I know). Get a transformer that is of a higher rating than what you estimate you need. Protection of the transformer is primarily performed by the circuit breaker or fuse protection on the main transformer feeder and the branch feeders powering the different loads in the building.

You really should be getting someone qualified to do this for you, is this for a cost estimating or tender proposal?

__________________
jack of all trades
Reply
Anonymous Poster
#2
In reply to #1

Re: installed power vs transformer rating

05/03/2009 9:17 PM

Thank you for prompt response.This is for verification purpose as the order had been placed for 100 kva.

Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: installed power vs transformer rating

05/04/2009 2:55 AM

dear,

Following may justify ?

Application : Residential , i.e. un balanced load.

Installed load : 190 KW

Power factor for L&F with ACs : 0.55 average.

Load factor : normally 0.45 , night times, with AC , 0.65

Demand on transformer : Normal - 155 kva , Peak - 224 kva

We suggest after derating with ambient., 250 KVA transformer minimum

with 200% Neutral for internal winding of transformer.

( unbalanced currents that can flow in neutral shall be 1.732 * Ir max.

__________________