For a marine vessel, where there is no neutral, we have 440V, 3 ph supply from owner.
We have a small 220V AC valve actuator.
I am only given the 440V, 3ph connection without neutral.
So how do I power up my actuator. Can someone please assist.
Thanks in advance.
Re: 440V 3Ph without neutral transform to 220V AC Single phase.
05/07/2009 3:00 AM
What is wanted is a transformer that takes the phase-to-phase voltage, and reduces it to 220VAC at its outlet terminals.
Suitable transformers are available from many sources.
Good Answers: 73
05/07/2009 9:06 AM
You want to buy a transformer that has a little higher KVA rating than the loads you are going to connect. If your valve is a 3 phase monster, you will need three transformers. I suspect it only has two wires and therefore is a single phase device.
Look for the current rating on the device label. Multiply it by 220 (volts) and you have the VA rating. Divide by 1000 and then you have the KVA rating. Don't forget that you will need to comply with electrical codes which means you will need some type of fuse or circuit breaker and a disconnect somewhere near the valve.