Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/09/2009 1:10 AM

Hi,

I have a machine which runs on 220v 60hz 3phase from Taiwan. I would like to use it in Singapore which is on 230v 50hz.

Will I have any problem?

Thank you!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#1

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/09/2009 1:31 AM

If its a motor only it would run just a bit slower, less power, and many get a little warmer. If electronics are involved it depends on the power supply and if any timing is supplied by line frequency it would be slower.

Best thing is to get in touch with the mfg. they could tell you what if any problems you could encounter.

Good luck

Charles

metalSmith's

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Reply Good Answer (Score 2)
Anonymous Poster
#2

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/09/2009 1:32 AM

dear

is it three phase 230 V 50hz supply in Singapure.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #2

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

07/19/2024 8:54 AM

That item can be looked up.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
2
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/09/2009 5:38 AM

There were quite a few discussions on this subject a few months back (then it was a hot topic )

To be very brief

a) For a motor V/f should be constant which will be the magnetizing flux for the iron.

For you it is 306 Vs 4.6 and a bit too away and hence the motor may not be up to it and not only the iron losses go up, but also may reach the inefficient or even saturated portion of the hysteresis curve

b) The motor will obviously run slower, This will further reduce the fan action and hence cooling

c) a+ b may simply burn off the windings, especially if it is to work near the rated capacity. Otherwise too, the efficiency is highly compromised.

The question is can you take the risk?

Just a link, is not much on this aspect, but the message is clear and loud in the end

https://www.hdp-power.com/sites/default/files/resources/kropla.com-Electric_Power_Around_The_World.pdf

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Good Answer (Score 2)
Member

Join Date: Dec 2008
Posts: 8
#4
In reply to #3

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/09/2009 10:44 PM

you can run this motor without any problem

same thing which done by me at our plant .

it is running without any problme

only the motor will run 10 to 15 % slow speed with its rated speed

speed = 120f/p

your voltage rating almost same.

and your phase is also same.

only the frequency is 50HZ

but if you rung 50hz motor with 60hz frequency then problem occure.

your motor life is decrease but in your case

its running wihtout any problem

you can do this..

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#12
In reply to #3

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/11/2009 9:33 AM

SB,

Another GA for you from me. One additional warning I wish to add though for the original poster.

Since the motor in question requires 3 phase, the expected work from this motor likely will not be small. So the 17% reduction in shaft power, speed, cooling etc. could easily be the difference between operation and smoke. If this is only a temporary rig that you (OP) can nurse along to prevent trouble, then I would say an attempt would be worthwhile. Just CYA by having everybody that uses this machine realize that this is a temporary kludge rig. If this is a permanent installation, then get the correct motor. Remember, you are not just providing torque for a machine with your motor choice. You are also establishing your reputation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Active Contributor

Join Date: May 2008
Posts: 17
Good Answers: 2
#5

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/09/2009 11:58 PM

Dear One,

You can use 230v ac,50hz in place of 220v,60hz, it will run bit lower and bir warmer, nothing will happed and you may not notice the difference,

Thanks

Reply
Anonymous Poster
#6

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/10/2009 1:02 AM

The motors ratings are not for normal operation and the device that uses the motor should have a voltage controller/regulator to take care of some of the problem of a potentially altered voltage. So.. the motor itself will be fine (albiet slightly slower), but you could possibly damage controls or any controller/regulator that might be wired and grounded differently in conjunction with the motor itself.

What is the device? That makes a huge difference...

Go for it.. If it fails, you know it was wrong. If it smokes from the speed control device, it was wired differently.. If it explodes and starts a fire.. get everyone out of the house/office/theatre... If it goes thermonuclear and you have a chance to pray.. Do it.

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#7

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/10/2009 1:46 AM

Guest,

A lot of people are saying "no problem". I disagree. SB has stated it well--see the other threads in the last few months on this topic. Depending on the application you may never have anything go wrong. But motors designed for use with both 50Hz and 60Hz always indicate their power output is lower on the 50Hz mains.

A worst case experience could be a motor failure leading to injury to people or damage to the plant. Investigation would show that it was an improper installation and the insurance company can then come back to you and charge you with negligence. Or someone dies and you get charged with their death. You then lose everything. "No problem"? Not hardly.

--JMM

Reply Score 1 for Good Answer
Power-User
Popular Science - Weaponology - Aerospace nut Hobbies - Musician - music enriches the soul United States - Member - Happy to be from the USA Engineering Fields - Acoustical Engineering - Pro Audio Speaker Designer Engineering Fields - Manufacturing Engineering - Aerospace ME Engineering Fields - Aerospace Engineering - Airplane nut from aeromodels to 747's

Join Date: Jul 2007
Location: Seattle WA
Posts: 113
Good Answers: 3
#11
In reply to #7

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/11/2009 8:51 AM

I have a similar problem but the inverse. I have a cylindrical grinder thats from England and is set up for 50hz. I don't have 3 phase so I am planning on using an inverter and am hoping I can get one that will convert 220/60hz 1 phase to the 50hz 3 phase that I need.

I haven't started investigating inverters but I assume that if its a rotary inverter you should be able to go from nearly any input to nearly any output as long as the total input/output are similar and your not trying to put a 10 hp motor on a 5 hp inverter.

__________________
The early bird gets the worm, but what about the early worm? A.E. Neuman
Reply
Power-User

Join Date: Sep 2007
Location: Scotland
Posts: 136
Good Answers: 5
#8

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/10/2009 8:52 AM

Yes you can. Perfectly safe and well within tolerances which should be posted on the device somewhere.

__________________
Stress? That's what you get when you do something interesting and worthwhile; if you can't handle it get out of the gene pool.
Reply
Associate
Jordan - Member - New Member

Join Date: Nov 2008
Posts: 27
Good Answers: 1
#9

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/10/2009 11:27 AM

i believe we should know more about that machine , coz so far everyone is talking about the motor problem, but only one mentioned that it depends on which kind of control on the machine u have also we need to know if you have valves or contactor coils that operate on the same line , also you have to be sure about that information of the 230V/50Hz as it can be 230V single phase & 380V three phase and that is very important .

we will wait to hear from you

Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#10
In reply to #9

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/11/2009 12:36 AM

It should be ok as far as supply and plug are concerned. You need tio check with download equipments for their suitability.

__________________
Best Regards, Shivaram
Reply
Associate

Join Date: Dec 2007
Location: Dubai
Posts: 32
Good Answers: 1
#13

Re: Can a machine using 220v 60Hz 3 phase be plug into a 230v 50hz plug

05/12/2009 4:44 AM

Motor will run, but with hot motor body and could lead to trip out. (check with infrared thermometer and observed)

Recommendation:

* to chage the motor or rewound based on site requirements

* if you cant afford to spend more bucks, you may opt to install fan/blower in order to reduce motor body heat but need continous observation and insure the sorrounding ambient teperature is cold.

FYI

__________________
nlp
Reply
Reply to Forum Thread 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amerlathqani (1); Anonymous Poster (2); jmueller (1); keshi123 (1); metalSmiths (1); nelson1 (1); pareshh_joshi (1); Philo (1); PWSlack (1); redfred (1); sb (1); shivaganti (1); snewkirk (1)