Grid parallel

05/09/2009 5:00 AM

When I put DG in grid parallel option, initially DG cannot take load, until I adjust the motorized POT. Why Dg cannot take load initially?? What is the reason?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Apr 2009
Location: ras al khaima
Posts: 25
#1

Re: Grid parallel

05/09/2009 1:19 PM

please specify about your load,name of the synchronizing controller and DG rating. load sharing depends on the pre set parameter on your controller. when generator sychronizied with grid, controller give commands to (avr and governor ) slowly take over the loads depend on the percentage which you set on your controller.

Register to Reply
Member

Join Date: May 2009
Posts: 5
#2
In reply to #1

Re: Grid parallel

05/10/2009 10:16 AM

Thanks for your reply!

1400Kw,SCGC controller.

I m adjusting manually by pot. what type of commend to give controller?what happen in alternator side at time of commend?

kindly tell me or send any soft copy in online?? pls

Register to Reply
Associate

Join Date: Apr 2009
Location: ras al khaima
Posts: 25
#3
In reply to #2

Re: Grid parallel

05/10/2009 12:24 PM

check your pot weather that is motorized or not. if motorized check, that is working properly or not. parameter setting for load sharing you have to call the panel supplier or technician from controller supplier. i have not idea about your controller. can you send me the manual for controller which you have mentioned.