Paralleling of distribution transformers

05/12/2009 6:18 AM

WHAT PRECAUTIONS DO WE NEED TO TAKE FOR PARALLELING OF DISTRIBUTION GRADE TRANSFORMERS - DYn11 configuration of windings. ( Assumed that the transformers have same polarity / Volt ratio / %Z impedence ) ? CAN WE PARALLEL THE NEUTRAL OF BOTH ? Can we connect them without on load tap changer unit + RTCC panel & AVR ?

How can we physically measure the circulating current ?

__________________
Exploring the Science of Electricity
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Paralleling of distribution transformers

05/12/2009 10:20 AM
  1. Turn off Caps Lock.
  2. Make sure the phase rotation of both is the same.
  3. Make sure the overcurrent protection on each winding is sufficient.
  4. Make sure the voltage output of each phase is the same.....
  5. Etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#2

Re: Paralleling of distribution transformers

05/13/2009 12:18 AM

If you need to ask, then answers given in a forum such as this wont help.

The risk of something loud and bright happening is too great, you'll need to pay for the services of an expert.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply
Active Contributor

Join Date: Sep 2007
Posts: 21
Good Answers: 1
#3

Re: Paralleling of distribution transformers

05/13/2009 2:14 AM

Is there any vector group DYn11? I think what the guy meant is Dyn11

Theoretically, the ideal conditions for paralleling transformers are as follows:

1. Identical turn ratios and voltage ratios otherwise a circulating current will flow, even at no-load

2. Equal % impedances

3. Equal ratios of resistance to reactance. If different, although there will be no circulating current at no-load, the applied load will not be shared proportional to their KVA ratings

4. Same polarity

5. Same phase angle shift

6. Same phase rotation

For the single-phase transformers, only the first four conditions apply as there's no phase rotation or phase angle shift

Practically I will advise you cosult professionals as someone has rightly advised.

__________________
One does not need a mirror to look at what one is wearing on the wrist
Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#4

Re: Paralleling of distribution transformers

05/13/2009 2:42 AM

Dear

I am assuming that secondary voltage of your Distribution Transformers are LT.

You have to check following things :

1 Vector group of both the transformers should be same.

2. Both the Transformers shaould have same voltage ratio at all the taps & when you run transformers in parallel, it should operate as same tap position.

3 If you have OLTC with RTCC panel, one RTCC should work as master & other should work as follower to maintain same tap positions of Transformer.

4. YOu must do synchronising check of both the supply voltages. This you can chech directly with multimeter between L1 phase of Trafo 1 & L1 phase of Trafo 2. Then L2 Phase of Trafo 1 & L2 Phase of Trafo 2. & then L3 Phase of Trafo 1 & L3 Phase of Trafo 2. In all the cases Multimeter should show 0 voltage theoritically. These checks you must do at synchromising breakers only. YOu have to also check that breaker out going terminals are connected in such a way that L1 Termianls of both the Breakers comes to same Main Busbar of panel. Same for L2 & L3.

5. YOu can install check synchronising relay & synchro scope also.

6. Best way to check syncronisation on LT is charge complete panel with 1 sourse up to out going terminals of another incoming breaker terminals. Then just measure Voltage difference on Incoming & out going termianals of Incoming Breaker. It should be near to 0.

7. To check circulating current Sunchronize both the trafos without out going load. Then check current. It will give you circulating current.

8. If Secondary of Trafo is not Lt then you must use check synchronising realay. & Commission the system properly. In brief, after connecting relay. remay must be charges with only 1 supply & check that realy is functioning poperly. They you can trust on wiring between relay & PT.

Register to Reply Score 1 for Good Answer
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#5

Re: Paralleling of distribution transformers

05/13/2009 7:00 AM

Hi there,

You are asking for a big bang if you want to parallel transformers are not sure what to look for!

Get hold of the electrical engineers handbook as well as the Network, Protection and Automation guide from Alsthom.

This will explain in great detail and more what you are looking for, and if you read it correctly - you will shy away from transformer paralleling.

Regards,

Craig

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#6

Re: Paralleling of distribution transformers

05/13/2009 7:03 AM

I always have that doubt, why people really parallel input and output both rather than going for a higher capacity ?

Whatever equality you try to maintain how you get rid of the circulating current ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#7
In reply to #6

Re: Paralleling of distribution transformers

05/13/2009 7:09 AM

I could not agree more with you my friend.

I have never, and will never undertake a job where you want me to parallel the two transformers. Rather they should have calculated the load correctly from the beginning and sized the transformer correctly with sufficient capacity for expansion.

That said, you will never ever have the same impedences between the two. It is impossible. Therefore - circulating current however small.

Cheers

Craig

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#8
In reply to #7

Re: Paralleling of distribution transformers

05/13/2009 7:18 AM

Or run non parallel (ie do not try to feed the same load) Take out a couple of motors and feed it by that.

In my factory shed itself, we had 1MVA sustation , expansion - another one is put. that was over last 25 Yrs.

Now recently for new expansion, we are putting a 2MVA and anyway the older ones being 25 yrs+ old, are being replaced with another 2MVA station.

But no paralleling, a zone is fed by one substation and another by different one. Nothing common (except the earthgrid)

I think people think if I can parallel the Generators, then why not transformers?

The basics are not understood ? In generators you struggle a lot to balance all your governors, AVRs and other controls are trying to make them equally share (and that too not much successfully, see so many posts)

And in transformer, you do not have any of these to equalize.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#10
In reply to #8

Re: Paralleling of distribution transformers

05/14/2009 1:06 AM

I could not agree more with you SB.

Split the load and run them individually.

As you say, paralleling generators is not the same as paralelling transformers. And I agree - there is alot that goes into paralleling genrators and getting them to work correctly.

By the way, I think the NPAG guide from Alsthom is a free download. It is well worh looking for working out your protection from generation, through distribution down to your actual motor.

Cheers

Craig

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#9

Re: Paralleling of distribution transformers

05/13/2009 12:00 PM

Do not forget that you will also double the available fault current. I have seen this as the limiting factor when transformers are to be operated in parallel.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#11
In reply to #9

Re: Paralleling of distribution transformers

05/15/2009 6:40 AM

HI GUYS!

ALL IS FINE, BUT YOU ALL HAVE NOT REPLIED

1. WETHER WE CAN PARALLEL NEUTRAL WIRES ALSO ?

2. WHAT PRECAUTION DO WE NEED TO TAKE ? ONLY REVERSE POWER RELAY WILL BE SUFFICE ? OR YOU NEED DIRECTIONAL OVER CURRENT & E/F RELAY ALSO ?

__________________
Exploring the Science of Electricity
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#12

Re: Paralleling of distribution transformers

05/18/2009 1:10 AM

Hi there,

I thought I did reply? GET HOLD OF THE ELECTRICAL ENGINEERS HANDBOOK as well as the NETWORK PROTECTION AND AUTOMATION GUIDE from Alsthrom. IT WILL EXPLAIN EVERYTHING YOU NEED TO KNOW ABOUT PARALLELING TRANSFORMERS AS WELL AS THE PRECAUTIONS AND PROTECTION ASSOCIATED THEREWITH!

Regards,

Craig

Register to Reply Score 1 for Off Topic
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#13

Re: Paralleling of distribution transformers

11/09/2010 9:40 AM

what is equal ratio of resistance to reactance? Do you mean series reactance and resistance in the equivalent circuit? if so how the currents on transformers change if % u are same? does it matter that they have different R/X ratio? Can you open this condition?

__________________
jinxnao
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ajay Patel (1); craigza (4); ffej (1); Goodho (1); harry potter (1); jinxnao (1); PWSlack (1); sb (2); solaaderinwale (1)

Previous in Forum: Spear sheath for Instrumentation Cable   Next in Forum: 10000 lux light for treatment of SAD

Advertisement