P.F Variations in two Gas Turbines in Synchronism

05/12/2009 12:24 PM

We have two GE Frame 5, 18 MW Gas Turbines running in parallel, in synchronism. The running load is about 14 MW on each Gas Turbine. One of the Gas Turbine is selected on ISO and other is on droop mode. Since the last one month, we are experiencing problem of variation in power factor. The p.f of one of the Gas Turbines falls to about 0.68, while that of the other rises to about 0.98. The load in Mega Watts remains unchanged. The reactive power of the gas turbine with lower p.f increases. The system voltage also increases from 6.3 kV to 6.42 kV. This lasts for 5 to 10 minutes and then normalizes by itself. Sometimes we also adjust the power factor ourselves by changing the excitation.

We have taken followings actions so far, without any success.

1) Cleaning of slip rings

2) Replacement of Carbon Brushes

3) Have checked the capacitors and electronic components of excitation system of one of the Gas Turbines in an opportunity.

4) The Gas Turbine on ISO was changed over to droop and vice versa. For 72 hours we also run both Gas Turbines on droop mode.

I would appreciate if some one can help us which Gas Turbine to suspect for the problem, possible causes, whether the problem can be outside the excitation system and tips for trouble shooting in synchronized condition.

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2009
Location: united states, california san francisco bay area native
Posts: 382
Good Answers: 8
#1

Re: P.F Variations in two Gas Turbines in Synchronism

05/12/2009 12:41 PM

is fuel metering filter clogged or dirty ?

__________________
give the hardest job to the laziest person & they'll find the easiest way to do it
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: P.F Variations in two Gas Turbines in Synchronism

05/12/2009 6:21 PM

The p.f is controlled by the AVR. So, you can have thorough check of the AVR systems of both GTG's including loose connection, configuration, settings etc.

What is the AVR make and model?

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Member

Join Date: May 2009
Posts: 5
#3

Re: P.F Variations in two Gas Turbines in Synchronism

05/13/2009 5:36 AM

If there was an intermittent problem with the droop CT input to the AVR, perhaps it would result in the AVR response being inconsistent with the load situation.