Anonymous Poster

Cable size

05/14/2009 12:13 AM

Can anyone please clarify that in a given size of cable (suppose 180 sq mm 3.5 core) what does the size represent, size of sinle core or overall size of cabel (all core plus insulation)?

Also if the current carried by a 3.5 core cable is 100 A, whether it is the current carried by each core or the overall current carried by all cores?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable size

05/14/2009 3:11 AM

<....(suppose 180 sq mm 3.5 core) what does the size represent, size of sinle core or overall size of cabel (all core plus insulation)?...>

The "180sq.mm" in the above description is the cross-section area [CSA] of one of the conductors. The "3.5" suggests that one of the conductors is smaller than the other three, and this particular one would be selected as the neutral conductor in a 3-phase circuit.

<....if the current carried by a 3.5 core cable is 100 A, whether it is the current carried by each core or the overall current carried by all cores?....>

It depends upon how the circuit is wired. In an everyday 3Ø supply situation, which is what this particular cable is intended for, the current that passes down one conductor comes back along the others.

The neutral is smaller because it only needs to carry:

  • the imbalance current between the other three phase conductors, or
  • a fault current for a very short period of time before the circuit protective device operates

so its CSA can be smaller without the risk of damaging the cable. At these sort of CSAs, the cable is going to have a lot of copper in it, which has a high value, and is going to be quite stiff, making it more difficult to bend round things during installation. Anything that can be done to reduce these difficulties safely is therefore worth considering.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Jan 2009
Location: Hyderabad
Posts: 8
#2

Re: Cable size

05/14/2009 3:14 AM

Dear Friend,

in each cable 100A ( i.e. 3 core cable having three wire with each phase 100A)

Regards

BVR

__________________
hyderabad
Reply
Anonymous Poster
#3

Re: Cable size

05/14/2009 6:15 AM

3.5 means 3 1/2 the half being size of neutral conductor. You can refer to my article on this - CABLE SIZES - at this location: http://docs.google.com/?hl=en&tab=wo&pli=1 questions? reach me on maintenance@maintenancecircle.com

Reply
Active Contributor

Join Date: Aug 2007
Posts: 11
#4

Re: Cable size

05/15/2009 6:25 AM

it should be the overall surface area of the copper

of course not incl the insulator, visit some cable manufacturer website and download their catalog, u will have a better picture. :)

Reply