Does using a AC MCB in a DC circuit affect the tripping time or the perfromance?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: M.C.B

05/15/2009 1:14 PM

It is not recommended. The reason is that the AC MCB utilizes the zero point of AC fault current to extinguish the arc to make the contact separation. If you use it in DC circuit, it fails and introduces hazard.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#2

Re: M.C.B

05/15/2009 4:16 PM

MCBs made by most major manufacturers have been tested and are rated for use in DC systems.

The maximum voltage will be considerably less than for AC, perhaps 50V per pole - best to consult manufacturer's datasheets for an exact figure. If you need to operate at a higher voltage, it is possible to connect multiple poles in series.

The current rating of an AC MCB in a DC system should be quite close to, if not the same as its rating in an AC system. The short-circuit current rating will be less in DC operation. Again, consult the manufacturer's datasheets.

Note that some manufacturers have several ranges of MCB, and may have only rated some of them for DC.