Why in three phase 440 circuit in all phase current is almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i check with clamp meter it shows 25 A?
The currents may be almost equal, but they need not be in phase.
The neutral current is the vector sum and not the scaler sum (or subtractions)
Assume the load power factors on different phases are different, then the currents will be unequally displaced in phase and you will have that readings, (ditto for voltage out of phase too)