Appliance Cables

05/17/2009 7:36 PM

what's the minimum cable size to accomodate appliances with 42.3kw. I am installing LCD which requires 42.3kw and the contractor proposed 95sq.mm. I think it is too big which I presume 70sq.mm will be sufficient enough. Please assist

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: cable size

05/17/2009 8:15 PM

No enough information. Voltage ? 3phase ? load power factor? length of the circuit ? What is LCD ?

Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 18
#2
In reply to #1

Re: cable size

05/17/2009 8:29 PM

100 amp, 3 phase & Liquid Crystal Digital (LCD)-Giant Screen

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3
In reply to #2

Re: cable size

05/17/2009 8:36 PM

What is the voltage? length of circuit estimate? where are you located? Are you using 3 single conductors + neutral or a cable with 3 conductors + neutral?

This chart gives the cable ampacity http://www.energy-solutions.co.uk/cable_conductor.html

Register to Reply
Anonymous Poster
#4

Re: Appliance Cables

05/19/2009 12:08 AM

Hi

I think 95 mm2 cable is too big for the installation . You can go for 4cx35 mm2 or 4cx50 mm2 cable size for the installation of LCD . XLPE/SWA cable to be used

Regards

Dhilju

Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#5

Re: Appliance Cables

05/19/2009 8:46 AM

Wareagle is quite correct to ask the questions he has. the distance question has to be answered to allow for voltage drop. The voltage question has to be answered for the same reason. The number of conductors and wether or not there is a neutral is also a question you must answer. He is trying to help you, help him to do this.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#6

Re: Appliance Cables

05/19/2009 9:13 AM

It may also be of interest to know what powerfactor this load has.

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: Appliance Cables

05/19/2009 11:12 AM

Apply your local standards. Your contractor to maintain his license should follow them, so should you. There are a myriad of concerns these standards consider besides just voltage drop. I will list a few rarely considered criteria that have made more than one installation to self destruct somewhere:

  • Added heat load effects in summer causing ignition.
  • Thermal expansion differences at splices while under a load during summer and winter.
  • Surge current
  • Insect damage
  • Future expansion
  • Insulation breakdown rate

This is not an exhausted list of the concerns. To say if your contractor is over or under sizing your installation, more information must be known about the installation that just the average load of one device.

P.S. What kind of an LCD system draws 42.3 kw of power?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Anonymous Poster
#8

Re: Appliance Cables

05/19/2009 11:37 AM

95 may seem overkill, but what about future expansion? A larger cable will mean less voltage drop and less resistance.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); capblanc (1); felixsemion (1); JIMRAT (1); redfred (1); wareagle (2)