what's the minimum cable size to accomodate appliances with 42.3kw. I am installing LCD which requires 42.3kw and the contractor proposed 95sq.mm. I think it is too big which I presume 70sq.mm will be sufficient enough. Please assist
Re: cable size
05/17/2009 8:15 PM
No enough information. Voltage ? 3phase ? load power factor? length of the circuit ? What is LCD ?
Re: cable size
05/17/2009 8:29 PM
100 amp, 3 phase & Liquid Crystal Digital (LCD)-Giant Screen
Re: cable size
05/17/2009 8:36 PM
What is the voltage? length of circuit estimate? where are you located? Are you using 3 single conductors + neutral or a cable with 3 conductors + neutral?
This chart gives the cable ampacity http://www.energy-solutions.co.uk/cable_conductor.html
Re: Appliance Cables
05/19/2009 12:08 AM
Hi
I think 95 mm2 cable is too big for the installation . You can go for 4cx35 mm2 or 4cx50 mm2 cable size for the installation of LCD . XLPE/SWA cable to be used
Regards
Dhilju
05/19/2009 8:46 AM
Wareagle is quite correct to ask the questions he has. the distance question has to be answered to allow for voltage drop. The voltage question has to be answered for the same reason. The number of conductors and wether or not there is a neutral is also a question you must answer. He is trying to help you, help him to do this.
Good Answers: 15
05/19/2009 9:13 AM
It may also be of interest to know what powerfactor this load has.
Chas
05/19/2009 11:12 AM
Apply your local standards. Your contractor to maintain his license should follow them, so should you. There are a myriad of concerns these standards consider besides just voltage drop. I will list a few rarely considered criteria that have made more than one installation to self destruct somewhere:
  • Added heat load effects in summer causing ignition.
  • Thermal expansion differences at splices while under a load during summer and winter.
  • Surge current
  • Insect damage
  • Future expansion
  • Insulation breakdown rate
This is not an exhausted list of the concerns. To say if your contractor is over or under sizing your installation, more information must be known about the installation that just the average load of one device.
P.S. What kind of an LCD system draws 42.3 kw of power?
05/19/2009 11:37 AM
95 may seem overkill, but what about future expansion? A larger cable will mean less voltage drop and less resistance.