Vacuum Drop - Code Requirements

05/21/2009 3:13 AM

This related to a Thermal Power Station (250MW). Vacuum in COndenser is created by one Vacuum pump which if stopped will cause gradual loss of vacuum and at a predetermined set value further operation of the Turbine is not allowed.

Can somebody guide me as what is the acceptable rate of vacuum drop - as per codal requirement. If U can send me reference document related to such an operational situation, it will help me.

Regards.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2007
Location: A secret. Bats are a Protected Species.
Posts: 186
Good Answers: 4
#1

Re: Vacuum Drop - as per codal requirement

05/21/2009 5:43 AM

The maximum vacuum is that which is related to the temperature of the condensate. So if you warm up the condensate then the vacuum will be lower.

Have you a set of steam tables to hand?

__________________
Innuendo is not Italian for a suppository.
Register to Reply
Participant

Join Date: May 2009
Location: Mumbai, INDIA
Posts: 3
#5
In reply to #1

Re: Vacuum Drop - as per codal requirement

05/25/2009 11:03 AM

Your reply is understood.

However, I am talking about RATE of Vacuum drop, i.e. mbar/min or inHg/ min.

This indicates as how leak-proof the plant vacuum system is and on loss of Vacuum pump, how long the turbine protection will take to become operative !

This RATE of vacuum drop is defined in HEI standard and my querry is related to the acceptable norm as per standard. From a normal vacuum of 29" Hg, it may take 20-25min when the vacuum level may reach the turbine protection set value.

Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#2

Re: Vacuum Drop - Code Requirements

05/23/2009 5:10 AM

Hi,

Your steam turbine will have been designed to operate into a specific vacuum. Any departure from this will reduce its efficiency according to a relationship between the starting steam pressure and the vacuum; basically you are looking at an operating range between 26 and 29 ''Hg. The poorer vacuum should be treated as a cut-off point where as anything above 29''Hg is a bonus(remember the effects of atmospheric pressure variation when watching a vac gauge reading.

You should therefore check with the turbine manufacturer to see what the design vacuum was and then set your evacuation system to cycle around that figure.

As the vacuum becomes weaker so the specific consumption of the turbine will increase so there is a penalty for operating with a low vacuum.

Hope this helps.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Participant

Join Date: May 2009
Location: Mumbai, INDIA
Posts: 3
#3
In reply to #2

Re: Vacuum Drop - Code Requirements

05/25/2009 1:12 AM

I appreciate your response. However, my querry was slightly different in nature.

Let me repeat the problem. We would be stopping the Vacuum pump at full load which would result in gradual drop in vacuum. Under this operating regime we intend to check the rate of drop in vacuum. This is not a normal operating condition.

QUERRY: What is the accepted rate of vacuum drop as per HEI code?

Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#4
In reply to #3

Re: Vacuum Drop - Code Requirements

05/25/2009 10:13 AM

Hi SKP,

I am not au fait with the HEI code and their website appears difficult to access. So can you give me the gist of the code in respect of this, please.

I do question the reason for what you are trying to achieve; is it because you suspect that your evacuator is having to do too much work? If so then you are trying to decide what action to take to reduce the quantity of air which is entering the steam system. Do you operate the gen plant on a 24/7 basis?

If you are experiencing a greater air problem now than in the past is it following an overhaul of the turbine? I'm thinking of mal-fitting shaft seals.Have you checked how the de-aerator(s) are working?

Look forward to hearing from you.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!