Ten Delta results to test insulation value

05/24/2009 12:40 AM

Can anybody help me how to conclude the status of insulation from the ten delta results and can we predict the life of the equipment from this value. since the equipments installed in swithchyard are very costly it is not fiesable to change them just because of poor ten delta result i.e beyond 2%

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#1

Re: Ten Delta results to test insulation value

05/25/2009 2:28 AM

normally, it is industrial prectice to get tested important equopment for ten delta value. But as per standard practice, with only one result it is not concluded healthyness of equipment. It is adviced to take ten delta values of critical equipment at the time of commissioing & that can be taken as reference. Thereafter, this values can be taken yearly or as per the suitablity. These resultas are to be compared with the reference results & we can monitor the detariation of the insulation of equipments by analising the different values taken at different time.

If this is your first reading, it will be taken as reference value & next reading will be used for analisis of the equipment.

Normally, the agancy who does the testing for you that will give you the analysis reports after studing all the results. Hence, it is prefered to get tested equipments with only one agancy preferably with same equipment for better analysis.

Register to Reply
Member

Join Date: May 2009
Posts: 5
#2
In reply to #1

Re: Ten Delta results to test insulation value

05/30/2009 6:29 AM

Its true that for analyses of insulation its history record is must . We are measuring ten delta of Current transformers above 15 years of age in service while taking the result in three or more steps it has been observed that the value of capacitance measured is not changing at 2Kv,4KV & 6KV & 10KV buit the measured ten delta value at 10KV rises abruptly to a value between 2 & 3 for lower test voltage its below the allowable limit that is below 1%.

Anurag

Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#3

Re: Ten Delta results to test insulation value

06/01/2009 2:24 AM

Agreed, but for analysis you must have historic values of the the results. ERDA is the best agency to do this tests & analysis also.

Or you can ask CT suppliers for analysis based on the test results. They can compare the test results with thrir other installations too.

Register to Reply
Member

Join Date: May 2009
Posts: 5
#4
In reply to #3

Re: Ten Delta results to test insulation value

06/02/2009 12:34 PM

thanks Ajay keep in touch.