05/23/2009 10:02 PM
Dear sir,
Can i use 110VAC coil for contactor designed for 220VAC coil ? or will it cause chattering while closing and openning of contacts.
Re: contactor
05/23/2009 10:25 PM
No. It is unlikely to even pull in the contacts. Check the datasheets of the contactor for minimum pickup and operation voltages.
Re: contactor
05/24/2009 1:57 AM
You can, provided these contactor remain same for different voltage coils as manufacture recommendation.
Coil size and fitment is ok
no chattering occurs
bye
Re: contactor
05/24/2009 11:16 PM
You can, but provided that your contactors are design for such coil changes. We always change our contactor coil from 110V to 220V. Our contactor and the contactor coil are standard design.
Re: contactor
05/25/2009 7:11 PM
contactor; go to the contactor rep or sales center and ask for a 120 volt coil to work for your contactor, many manufactures make a 110 volt 50 HZ/120 volt/60 HZ, 208 volt, 240 volt , 277, 415, 460, 480, 600 volt coils to work in their contractors. perry
Re: contactor
05/26/2009 3:34 AM
So long as the supply voltage and the coil voltage are the same, there shouldn't be any issue.