Anonymous Poster

contactor

05/23/2009 10:02 PM

Dear sir,

Can i use 110VAC coil for contactor designed for 220VAC coil ? or will it cause chattering while closing and openning of contacts.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: contactor

05/23/2009 10:25 PM

No. It is unlikely to even pull in the contacts. Check the datasheets of the contactor for minimum pickup and operation voltages.

__________________
jack of all trades
Reply
Active Contributor

Join Date: May 2008
Posts: 17
Good Answers: 2
#2

Re: contactor

05/24/2009 1:57 AM

You can, provided these contactor remain same for different voltage coils as manufacture recommendation.

Coil size and fitment is ok

no chattering occurs

bye

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: contactor

05/24/2009 11:16 PM

You can, but provided that your contactors are design for such coil changes. We always change our contactor coil from 110V to 220V. Our contactor and the contactor coil are standard design.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#4

Re: contactor

05/25/2009 7:11 PM

contactor; go to the contactor rep or sales center and ask for a 120 volt coil to work for your contactor, many manufactures make a 110 volt 50 HZ/120 volt/60 HZ, 208 volt, 240 volt , 277, 415, 460, 480, 600 volt coils to work in their contractors. perry

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: contactor

05/26/2009 3:34 AM

So long as the supply voltage and the coil voltage are the same, there shouldn't be any issue.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply