star delta motor problem

05/24/2009 1:32 PM

One of my 60 hp motor is showing proper resistance. once i start it, its getting start in star mode and tripping in delta mode. what will be the reason. please guide me as i am not a electrical engg.

__________________
thoughts becomes things.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: star delta motor problem

05/24/2009 3:07 PM

What is tripping, the Overload Relay or the Circuit Breaker?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: star delta motor problem

05/24/2009 9:33 PM

Check the current settings.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: star delta motor problem

05/24/2009 10:57 PM

It this is a new connected motor or the existing motor ?

If it is an existing motor, do you have any problem starting it previously?.

We also want to know if you have change the load, for example last time it was to run a small pumps and now you have change the pump slightly bigger and so on....

What is the load this motor connected to?

What is the timer set for the contactor changeover to Delta point. You can see the timer set inside the control panel.

Please let us have these information.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: star delta motor problem

05/24/2009 11:42 PM

What I believe is that this is a normal starting method of 3-ph A/C motors, since it is still running.

Register to Reply
2
Anonymous Poster
#5

Re: star delta motor problem

05/24/2009 11:52 PM

As well as all the other good suggestions, if it is tripping the circuit breaker protection (you did not exactly say what was tripping) as soon as the changeover happens you should check for incorrect connection of the six motor leads - it may be attempting to reverse the direction of rotation.

It is a long time since I had anything to do with star-delta starters, but if this turns out to be the problem I could probably help with a procedure to solve teh problem. You would as a minimum need to ensure all six leads are connected correctly as best you can, then if that is no help due to no marking on cables or incorrect marking, you will need to disconnect all six , and start from scratch with continuity-checks of the motor windings to separate out the 3 circuits (one circuit per phase).

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Feb 2006
Posts: 55
#7
In reply to #5

Re: star delta motor problem

05/25/2009 1:09 AM

Most of the time this is the problem you need a multy meter to check the continutie of 6 leads mentioned good luck

crm

Register to Reply
Anonymous Poster
#6

Re: star delta motor problem

05/25/2009 12:55 AM

My dear friend ,

I have this problem before and I'm sure the connection to the the motor in the power circuit has two wires are awapped.

If you need my advice , just swap two wires from delta connection.

Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#8

Re: star delta motor problem

05/25/2009 2:39 AM

Please also see that

1. Change over From Stat To CDelta must happen when currunt in star falls down.

2. Disconnect Cables from Motor terminals & take Trial of Starter keeping all cables at safe distance. If the starter is nottripping then the problem is in formation of Star. This can be in side the starter & even at motor terminals also.

3. Check current when starter falls in Delta, check whether all three phase is taking current or not. If problem in formation of Delta, one of thep hase will not draw current.

Register to Reply
Member
Philippines - Member - New Member

Join Date: May 2009
Posts: 6
#9

Re: star delta motor problem

05/25/2009 3:16 AM

First and formost check the polarity of the six leads terminal and set this aside if you have already determine the correct polarity. then check the control circuit on the delta load side contactor trace the connection moving up to the wye loadside contactor up to the line supply side. the change over timer is just a matter of adjustment the required time delay as you wish but should not long than 10 seconds. Probably the problem is on the delta contactor. thats all, good luck.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: star delta motor problem

05/25/2009 11:37 AM

First and foremost you must determine what is tripping! If it is tripping on Overload, that is a completely different problem that if t is tripping the circuit breaker. Any advice without knowing that is potentially steering you in the wrong direction.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Member
Philippines - Member - New Member

Join Date: May 2009
Posts: 6
#13
In reply to #10

Re: star delta motor problem

05/26/2009 5:03 PM

The tripping known that occur during change over from star to delta. it is probably in the wrong connection on the deta side, might be on either one or two winding naturally it will trip the overload relay of delta contactor, since both relay are in series with star relay otherwise it will not start if it wrong polarity in star connection, it is during the change over. if the polarity is wrong during change over, the effect sudden reverse which is contradict and the current will increase tend to trip the relay before the breaker, since the relay has set to smaller current than the breaker which is capable to handle up to 10kampere of minimum rating in a split of second. try to analyze the characteristic between the breaker compare to a relay. and compare this to a trasformer of wrong polarity connection, if you want a more detail, it is not whom you know but what you know.

Register to Reply
Participant

Join Date: Mar 2009
Location: Edmonton, Alberta Canada
Posts: 3
Good Answers: 1
#11

Re: star delta motor problem

05/25/2009 12:21 PM

As pointed out by a number of very intelligent people already the need to check proper rotation and phasing in Delta mode is important. The timing of the drop out of the star connector and the pickup of the delta connector is also critical. Based on one article you want sufficient time for the arc on the start contactor to extinguish prior to picking up the delta connector.

__________________
Tell me I'll forget, Show me I may remember, Involve me and I will understand
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#12

Re: star delta motor problem

05/26/2009 2:21 AM

Mr.JRaef is right.

"First and foremost you must determine what is tripping! If it is tripping on Overload, that is a completely different problem that if t is tripping the circuit breaker. Any advice without knowing that is potentially steering you in the wrong direction."

The main problem is that no one know whether the motor is the existing motor that had been in operating previously and suddenly it give your the problems or it is a new installed motor. If it is a existing motor, then all the information given will be misleading to solve the problem.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Anonymous Poster
#14

Re: star delta motor problem

05/27/2009 2:01 AM

check the change over time from star to delta,the motor should at least attained 80% of the fullload before change.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#15

Re: star delta motor problem

08/09/2009 9:58 AM

ok i also fasing same probs.so do 1 thing cahnge ur relat..u using 10A class relay..right.. so change with 20 A class relay..by usung this relay u change ur tripping time..ok

Register to Reply
Anonymous Poster
#16

Re: star delta motor problem

12/02/2009 7:42 AM

YOUR PHASE SEQUENCE IS NOT CORRECT.

Register to Reply
Member

Join Date: Aug 2015
Posts: 6
#17

Re: star delta motor problem

09/01/2015 1:24 AM

i agree with most of the answers..the problem which i think so can be with timer which shift the star delta connection.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: